Can we calculate the timer setting for changeover from star to delta from the design-code letter of the motor?. Please give an example under a)no load b)half load c)full load conditions.
Asked by naban on 10/19/2011 3:32:37 AM
The Best Answer
profileimage
Steven
Questions:1
Answers:42
Best Answers:12
The changeover time is not a single figure and you need an understanding of the starting time to be able to set the changeover timer. It depends on the inertia of the load, the accelerating torque and other factors. For each application it is going to be different. For example the starting time for a mine shaft high inertia ventilation fan could be 30 seconds plus, whereas a fan in an air-conditioning unit would reach full speed in a fraction of this time.

Understanding the starting could be by calculation or measurements in the field.
Answered by Steven on 12/22/2011 2:57:31 AM
2 0

To answer a question you need to Login

Your Email:
We respect your email privacy


Most Popular Notes:

Low Voltage Switchroom Design Guide

Standard Cable & Wire Sizes

DC Motor Operation

Medium Voltage Switchgear Room Design Guide

Restricted Earth Fault Protection

Maximum Demand Estimation

Three Phase Power Simplified

Material Properties


Unsolved Questions:

  1. Refers to cable sizing tool 10th line. Is it : No of cables/circuit ?
  2. How to calculate the temp. a cable will reach?
  3. Isolating 400V generator busbar with 400V station supply.
  4. Help me size this motor cable?
  5. What is a current tranformer class?
  6. Limitation of AC Submarine Cable
  7. Mobile Electrical Equipment Room Standards?
  8. Time Current Curve Equations for MCBs
  9. What is the difference between restricted earth fault relay and stand by earth fault relay?
  10. Why we use the 1A OR 5A in current transformers, which one is the prefferable for end user and application?
  11. Why transformer does not rotate like induction motor. while both having same principle?
  12. Effect of voltage drop on induction motor current

more questions...
Copyright (c) 2012 myElectrical Terms Of Use Privacy Statement Advertise Contact Us