When to use direct on line starting or star-delta starting on an electric motor? Does it depend on the capacity of the motor itself?
Asked by dody_indra on 11/15/2011 9:33:35 PM
The Best Answer
profileimage
Steven
Questions:1
Answers:42
Best Answers:12
It does not really depend on the size, but on the system it’s self. I have started some very large motors DOL. Some regulations/authorities do request motors above a certain size (3 kW or similar) to use star-delta. My understanding is that regulations like this are a bit of a make it easy and safe type of thing; with most of the authorities allowing deviations given sufficient technical justification (no guarantees though).

There are also a couple of posts on the site you may want to look at:

Direct On Line - http://myelectrical.com/opinion/entryid/79/motor-starting-direct-on-line
Star Delta - http://myelectrical.com/opinion/entryid/83/motor-starting-star-delta

Answered by Steven on 11/17/2011 8:02:19 AM
2 0
profileimage
dody_indra
Questions:2
Answers:1
Best Answers:0
Ok thanks a lot about your answer
Answered by dody_indra on 11/17/2011 8:26:37 PM
0 0

To answer a question you need to Login

Your Email:
We respect your email privacy


Most Popular Notes:

Low Voltage Switchroom Design Guide

Standard Cable & Wire Sizes

DC Motor Operation

Medium Voltage Switchgear Room Design Guide

Restricted Earth Fault Protection

Maximum Demand Estimation

Three Phase Power Simplified

Material Properties


Unsolved Questions:

  1. Refers to cable sizing tool 10th line. Is it : No of cables/circuit ?
  2. How to calculate the temp. a cable will reach?
  3. Isolating 400V generator busbar with 400V station supply.
  4. Help me size this motor cable?
  5. What is a current tranformer class?
  6. Limitation of AC Submarine Cable
  7. Mobile Electrical Equipment Room Standards?
  8. Time Current Curve Equations for MCBs
  9. What is the difference between restricted earth fault relay and stand by earth fault relay?
  10. Why we use the 1A OR 5A in current transformers, which one is the prefferable for end user and application?
  11. Why transformer does not rotate like induction motor. while both having same principle?
  12. Effect of voltage drop on induction motor current

more questions...
Copyright (c) 2012 myElectrical Terms Of Use Privacy Statement Advertise Contact Us