3 core vs 3 and half core
profileimage
santanu
Questions:2
Answers:0
Best Answers:0
What is the difference in construction and in properties between 3 core cable, 3 and half core cable and 4 core cable?
Asked by santanu on 12/23/2011 12:57:11 AM
The Best Answer
profileimage
Steven
Questions:1
Answers:42
Best Answers:12
Three core cables are normally used for balanced loads (L1, L2 and L3). A four core cable would be used for loads where a neutral is required (L1, L2, L3 and N). Often the neutral will carry significantly less current than the line conductors (in a balanced system it should be zero) and a half sized neutral is used to save copper (three and a half cores).

Note: normally I would specify a three core cable for balanced loads (i.e. motors) and a four core cable for distribution; I’m not a big fan of the half core. In some instances (where there are a lot of harmonics for example), you would be looking at a neutral current which exceeds the line current and a double sized neutral.
Answered by Steven on 1/8/2012 7:56:03 AM
2 0

To answer a question you need to Login

Your Email:
We respect your email privacy


Most Popular Notes:

Low Voltage Switchroom Design Guide

Standard Cable & Wire Sizes

DC Motor Operation

Medium Voltage Switchgear Room Design Guide

Restricted Earth Fault Protection

Maximum Demand Estimation

Three Phase Power Simplified

Material Properties


Unsolved Questions:

  1. Refers to cable sizing tool 10th line. Is it : No of cables/circuit ?
  2. How to calculate the temp. a cable will reach?
  3. Isolating 400V generator busbar with 400V station supply.
  4. Help me size this motor cable?
  5. What is a current tranformer class?
  6. Limitation of AC Submarine Cable
  7. Mobile Electrical Equipment Room Standards?
  8. Time Current Curve Equations for MCBs
  9. What is the difference between restricted earth fault relay and stand by earth fault relay?
  10. Why we use the 1A OR 5A in current transformers, which one is the prefferable for end user and application?
  11. Why transformer does not rotate like induction motor. while both having same principle?
  12. Effect of voltage drop on induction motor current

more questions...
Copyright (c) 2012 myElectrical Terms Of Use Privacy Statement Advertise Contact Us