Formula for Knee Point voltage calculation of a132/11kV CT
profileimage
chandanasushma
Questions:5
Answers:0
Best Answers:0
I have been using 800-400-200/1-1-1-1-1A CT with three class PS cores,5P10-20VA and 0.2-20VA.How to find knee point voltage and its burden. My supplier cannot provide the data. Its given by APTRANSCO that transformer differential protection has a formula of 40I(Rct+10). Please explain me the terminology and procedure. So I need your help sir.
Asked by chandanasushma on 9/26/2011 7:39:09 AM
profileimage
Steven
Questions:1
Answers:42
Best Answers:12
CT can be specified according to IEC or BS. The formulae you have looks like the one to convert from IEC to BS. The Siemens Power Engineering Guide (you can search for and download), gives the conversion as:

Uk = In * Kssc * (Rct + Rb) / 1.3

Uk = knee voltage
In = nominal current (1 A in your case)
Kssc = rated symmetrical short-circuit current factor (i.e. 5P10 -> 10)
Rct = secondary winding resistance
Rb = rated resistive burden (20 VA in your case)

Uk = 1 * 10 * (Rct + 20) /1.3

This does not tie up with the formulae you gave, so I’m thinking there is something wrong. Perhaps you should ask APTRANSCO where they got their formulae from.
Answered by Steven on 9/27/2011 7:12:57 AM
4 0

To answer a question you need to Login

Your Email:
We respect your email privacy


Most Popular Notes:

Low Voltage Switchroom Design Guide

Standard Cable & Wire Sizes

DC Motor Operation

Medium Voltage Switchgear Room Design Guide

Restricted Earth Fault Protection

Maximum Demand Estimation

Three Phase Power Simplified

Material Properties


Unsolved Questions:

  1. Refers to cable sizing tool 10th line. Is it : No of cables/circuit ?
  2. How to calculate the temp. a cable will reach?
  3. Isolating 400V generator busbar with 400V station supply.
  4. Help me size this motor cable?
  5. What is a current tranformer class?
  6. Limitation of AC Submarine Cable
  7. Mobile Electrical Equipment Room Standards?
  8. Time Current Curve Equations for MCBs
  9. What is the difference between restricted earth fault relay and stand by earth fault relay?
  10. Why we use the 1A OR 5A in current transformers, which one is the prefferable for end user and application?
  11. Why transformer does not rotate like induction motor. while both having same principle?
  12. Effect of voltage drop on induction motor current

more questions...
Copyright (c) 2012 myElectrical Terms Of Use Privacy Statement Advertise Contact Us