Formula for Knee Point voltage calculation of a132/11kV CT
chandanasushma
Questions:5
Answers:0
Best Answers:0
I have been using 800-400-200/1-1-1-1-1A CT with three class PS cores,5P10-20VA and 0.2-20VA.How to find knee point voltage and its burden. My supplier cannot provide the data. Its given by APTRANSCO that transformer differential protection has a formula of 40I(Rct+10). Please explain me the terminology and procedure. So I need your help sir.
Asked by chandanasushma on 9/26/2011 7:39:09 AM
Steven
Questions:1
Answers:42
Best Answers:12
CT can be specified according to IEC or BS. The formulae you have looks like the one to convert from IEC to BS. The Siemens Power Engineering Guide (you can search for and download), gives the conversion as:
Uk = In * Kssc * (Rct + Rb) / 1.3
Uk = knee voltage
In = nominal current (1 A in your case)
Kssc = rated symmetrical short-circuit current factor (i.e. 5P10 -> 10)
Rct = secondary winding resistance
Rb = rated resistive burden (20 VA in your case)
Uk = 1 * 10 * (Rct + 20) /1.3
This does not tie up with the formulae you gave, so I’m thinking there is something wrong. Perhaps you should ask APTRANSCO where they got their formulae from.
Answered by Steven on 9/27/2011 7:12:57 AM
4
0
To answer a question you need to Login
Your Email:
We respect your email privacy
Most Popular Notes:
Low Voltage Switchroom Design Guide
Standard Cable & Wire Sizes
DC Motor Operation
Medium Voltage Switchgear Room Design Guide
Restricted Earth Fault Protection
Maximum Demand Estimation
Three Phase Power Simplified
Material Properties
Unsolved Questions:
Refers to cable sizing tool 10th line. Is it : No of cables/circuit ?
How to calculate the temp. a cable will reach?
Isolating 400V generator busbar with 400V station supply.
Help me size this motor cable?
What is a current tranformer class?
Limitation of AC Submarine Cable
Mobile Electrical Equipment Room Standards?
Time Current Curve Equations for MCBs
What is the difference between restricted earth fault relay and stand by earth fault relay?
Why we use the 1A OR 5A in current transformers, which one is the prefferable for end user and application?
Why transformer does not rotate like induction motor. while both having same principle?
Effect of voltage drop on induction motor current
more questions...
Copyright (c) 2012 myElectrical
Terms Of Use
Privacy Statement
Advertise
Contact Us