Power that can be used on copper wire

Could you help me on the equivalent current of three phase alternating current having 400V , 530kW and the available cross-sectional area of a copper wire. Its length 350m for carrying this current.
asked 7/2/2012
0

1 Answer

To work out the current, you need the power factor (and efficiency if it is a motors, as your kW is the output power): 

Current = 530,000/(3x230xpower factor), at a power factor of 0.95 = 808 A

To understand the calculation, you can read the post: Three Phase Current - Simple Calculation 

The cable size depends on the installation method and what voltage drop you will accept.

You can use the sites cable sizing tool to work this out.

answered 7/4/2012 Steven McFadyen 199
Steven McFadyen

Your Answer

In order to provide an answer to this question, you must Login

I am flagging this question because...




10 inform moderator flags remaining

I am deleting this question because...




I am flagging this answer because...




10 inform moderator flags remaining

Flagging a Post

You have already flagged this post. Clicking "Remove Flag" below will remove your flag, thus reducing the count by one as well.

I am deleting this answer because...





Latest Questions:

  1. Power Transformer Temperature Measurement
  2. Voltage Conversion
  3. Arc Flash
  4. Voltage Transformer
  5. Earth Leakage Protection for 3 Phase Motor (Rating < 5.5kw)
  6. Power Swing
  7. Grounding Transformers above Ground Level
  8. Current Carrying Capacity of Cables

most popular notesMost Popular Notes:







newsletter logo

Our Newsletter

Receive updates on new posts by email
down arrow


myElectricalEngineering.co.uk
Our website uses cookies so that we can provide a better experience.
To learn more about what cookies are and how to manage them visit AboutCookies.org