Formula for Knee Point voltage calculation of a132/11kV CT

  • Up
  • Down
I have been using 800-400-200/1-1-1-1-1A CT with three class PS cores,5P10-20VA and 0.2-20VA.How to find knee point voltage and its burden. My supplier cannot provide the data. Its given by APTRANSCO that transformer differential protection has a formula of 40I(Rct+10). Please explain me the terminology and procedure. So I need your help sir.
Protection
Term: Protection
aboutimprove description
Current Transformers
Term: Current Transformers
aboutimprove description
asked 9/26/2011
chandanasushma1
chandanasushma

3 Answers

  • oldest
  • active
  • votes
  • Up
  • Down
The formula for calculating the knee point voltage of a PS Class CT is:

Vkp > K * If (r) (Rct + Rb)

where,

Vkp = The minimum Knee Point Voltage of the CT
K = Safety factor, generally taken as 2
If (r) = Maximum Anticipated fault current, as reflected on the CT Secondary side
= Maximum anticipated primary fault current /CT Ratio
Rct = Secondary Winding Resistance of the CT
Rb = Two way lead burden of the wires from CT Secondary to the relay
answered 1 month ago EE65 17
EE65
  • Up
  • Down

According to the answer from Sir Steven ,

I think there may be a point need to be confirmed :

About the Rb , Sir Steven said  : Rb = rated resistive burden (20 VA in your case)

and what i understand is Burden = Isn^2 *Rb

In this case Isn=1A, so the Burden =1^2*Rb, Rb is equal to the value of rated burden .

when the Isn=5A, the Burden=5^2*Rb , the Rb = burden/ 25

Please have a check .

Thank you very much .

 

answered 7/10/2012 Qian Minchun 2
Qian Minchun
  • Qian,

    You logic is correct in calculating the resistance of a device burden.

    Re-reading the question and my previous answer, maybe the terminology is not fully clear. Relays have a burden which can be expressed in VA (or resistance according to your formulae). Total burden of a relay circuit is that presented by both the relay and the connecting wirings. Total burden connected to the current transformer is the sum of each individual relay circuit burden for all the connected relays.

    The current transformers supply the necessary VA for the total connected burden. For a 20 VA current transformer, it can supply a total connected burden of 20 VA (or total connected resistance of 0.8Ω at 5A).

    Steven - Steven 7/10/2012

  • Up
  • Down
CT can be specified according to IEC or BS. The formulae you have looks like the one to convert from IEC to BS. The Siemens Power Engineering Guide (you can search for and download), gives the conversion as:

Uk = In * Kssc * (Rct + Rb) / 1.3

Uk = knee voltage
In = nominal current (1 A in your case)
Kssc = rated symmetrical short-circuit current factor (i.e. 5P10 -> 10)
Rct = secondary winding resistance
Rb = rated resistive burden (20 VA in your case)

Uk = 1 * 10 * (Rct + 20) /1.3

This does not tie up with the formulae you gave, so I’m thinking there is something wrong. Perhaps you should ask APTRANSCO where they got their formulae from.
answered 9/27/2011 Steven 167
Steven

Your Answer

In order to provide an answer to this question, you must Login

I am flagging this question because...




  • Flag
10 inform moderator flags remaining

I am deleting this question because...




  • Delete

I am flagging this answer because...




  • Flag
10 inform moderator flags remaining

Flagging a Post

You have already flagged this post. Clicking "Remove Flag" below will remove your flag, thus reducing the count by one as well.

  • Remove Flag

I am deleting this answer because...




  • Delete
327
57


Latest Questions:

  1. Transformer fault
  2. NJATC Theory Trainer
  3. Neutral Earthing
  4. New Electrician
  5. Three Phase Motor Calculation
  6. Bus bar sizing
  7. Protection plan for a transformer
  8. diffenrce between 64REF, 64 and 51N

more questions...

Most Popular Notes:

Three Phase Current - Simple Calculation

Motor Starting - Star Delta

Switchboard - Forms of Internal Separation

Standard Cable & Wire Sizes

Restricted Earth Fault Protection

Cable Sizing Tool

Motor Starting - Direct On Line

Electromagnetic Compatibility (EMC)


more notes...


Your Email:
We respect your email privacy

Copyright (c) 2013 myElectrical Terms Of Use Privacy Statement Advertise Contact Us