MCCB Selection

I have 3 phase 220V domestic power supply to my home by 16 mm aluminium 4 core armored cable. I have a sanction of 15KW load. With a concern for safety I intend to retrofit a MCCB of suitable rating. Request you to please guide me with respect to Amperage, Icu 240V, Icu 410V & Ics 415 V ratings required for the MCCB.

Let me know if you require any additional information.


 


asked 4/19/2016
Sandeep Dogra2
Sandeep Dogra

2 Answers

kVA = kW/0.8P.F

kVA = 15/0.8

kVA = 18.75kVA

I = kVA/(1.732x415V)

I = 18.75/718.78

I = 0.0260kA

I = 26A

I = 26A x 1.2 (overload factor)

I (MCCB,TP) = 32A   Icu = 10kA and Ics = 6kA will be more then enough.

32A MCCB, TP as Incoming breaker 

Further outgoing breakers for 220V system could be MCCB's, DP or SP as per requirement.

 

 

 

answered 2 months ago حسان نوابی 2
حسان نوابی

Hi friend,

            As per your given details MCCB is not required MPCB is enough. But you have MCCB for this load you chose the 50 A MCCB for 220 V. For 415 V 32 A MCCB is enough.    

 I=P/(SQRT(3)*220*0.85))       You take your loads I=15000/(1.732*220*0.85) it comes 46 A you take 15% extra 50 A MCCB is enough.

answered 6/16/2016 Dinesh137 2
Dinesh137

Your Answer

In order to provide an answer to this question, you must Login

I am flagging this question because...




10 inform moderator flags remaining

I am deleting this question because...




I am flagging this answer because...




10 inform moderator flags remaining

Flagging a Post

You have already flagged this post. Clicking "Remove Flag" below will remove your flag, thus reducing the count by one as well.

I am deleting this answer because...







myCableEngineering.com - the complete application for managing, engineering and sizing your cables.







newsletter logo

Our Newsletter

Receive updates on new posts by email
down arrow

Our website uses cookies so that we can provide a better experience.
To learn more about what cookies are and how to manage them visit AboutCookies.org