How can we calculate Breaking Capacity of Circuit Breaker

asked 12/23/2011

2 Answers

we cant able to calculate breaking capacity of breaker due to is deponds of the breaker manufacturing as per iec rules ... it is the with stand capacity of the breaker ,, there is only the chance to calculate breaker withstand capacity by interms of transformer MVA rating....
answered 3/24/2012 trex 1
The breaking capacity is normally specified by the manufacturer. To have this rating verified the breaker had to undergo a series of tests. There is also a post on the site which you can look at:

If you want to know which breaker rating to select, you need to calculate the anticipated fault level and then select the next highest rating. IEC 60909 gives guidance on how to go about calculating the anticipated fault level (and there are other methods/tutorials around if you search for them).
answered 1/8/2012 Steven McFadyen 232
Steven McFadyen

Your Answer

In order to provide an answer to this question, you must Login

I am flagging this question because...

10 inform moderator flags remaining

I am deleting this question because...

I am flagging this answer because...

10 inform moderator flags remaining

Flagging a Post

You have already flagged this post. Clicking "Remove Flag" below will remove your flag, thus reducing the count by one as well.

I am deleting this answer because...

Latest Questions:

  1. Electrcial Distribution Cabinets B15
  2. Breakers
  3. Cable AC Resistance calculation
  4. Induction Machine Types
  5. Zone Delimiters in distribution network
  6. Voltage level
  7. Lightning Protection calculation Free Software
  8. How many motors, or of what kind, do I need to get the output to be 5 Volts under load?

most popular notesMost Popular Notes:

newsletter logo

Our Newsletter

Receive updates on new posts by email
down arrow

Our website uses cookies so that we can provide a better experience.
To learn more about what cookies are and how to manage them visit