Grading across a transformer

I wanted to verify my understanding was correct, that owing to the delta/star winding of most LV transformers, the fault level seen by the HV protection is 2/3 the fault level(converted to current at the primary voltage) as the fault experienced at LV for both 2phase and 3phase faults.

I came across this info in a power system commissioning book published by theIEE; however am confused that this does not appear to be taken into consideration by software packages.

If correct, then it would suggest the HV time current curve should be moved tothe right of the LV curves when they are displayed together and you are assessing discrimination across a transformer  with the fault immediately downstream on the main LV protective device...




asked 9/26/2012
Rhys Jones2
Rhys Jones

2 Answers

You are a wee-bit incorrect, I am afraid. In a delta connected primary of a delta/star trafo., only the phase current (i.e.) the current thro the windings would be about 56% of the line current. But, the protection system, even on the HV side, would only see the line current, which would be reduced at the HV side, by the turns ratio of the trafo.

Why then, there should be a problem in co-ordination?
answered 4/10/2013 EE65 19
EE65

Not sure where 2/3 comes from; it doesn't sound right to me. I think the primary fault level would be related to turns (voltage) ratio of the transformer. If you have for example a 240 MVA fault on the secondary, it will still be seen as a 240 MVA on the primary. The difference will be in the level of current (the secondary current being much bigger and the actual value being dependent on the voltages).

If you can post an extract from the book, I can try to work out where to 2/3 came from.

On protection curves, you are right - you do need to make sure all the curves are related to the same voltage (which would mean shifting any HV curves to the right on an LV plot).
answered 9/30/2012 Steven McFadyen 246
Steven McFadyen

Your Answer

In order to provide an answer to this question, you must Login

I am flagging this question because...




10 inform moderator flags remaining

I am deleting this question because...




I am flagging this answer because...




10 inform moderator flags remaining

Flagging a Post

You have already flagged this post. Clicking "Remove Flag" below will remove your flag, thus reducing the count by one as well.

I am deleting this answer because...





Introduction to Cathodic Protection

If two dissimilar metals are touching and an external conducting path exists, corrosion of one the metals can take place.  Moisture or other materials...

Surface Treatment – Ladders, Trays and Baskets

Steel ladders, trays and baskets form the backbone of cable containment systems. Often these items need some form of surface treatment to prevent corrosion...

Back to Basics - Ohm’s Law

Electrical engineering has a multitude of laws and theorems. It is fair to say the Ohm's Law is one of the more widely known; it not the most known. Developed...

Getting Started with Patents

If you have a great idea or invent something the last thing you want is someone to steal the idea. One of the things you can do is protect the intellectual...

Tip – Latitude and Longitude on Large Scale Plans

If you are working on a large plan, get the real coordinates [latitude, longitude] for two or more points and add them to the drawing. That way you can...

Fire Resistant and Fire Retardant Cables

Fire resistant and fire retardant cable sheaths are design to resist combustion and limit the propagation of flames. Low smokes cables have a sheath designed...

Gas Insulated or Air Insulated Switchgear

Various arguments exist around SF6 Gas Insulated (GIS) and Air Insulated (AIS) medium voltage switchgear. Recently we had to change a GIS design to AI...

Dielectric loss in cables

Dielectrics (insulating materials for example) when subjected to a varying electric field, will have some energy loss.   The varying electric field causes...

Power Factor

Power factor is the ratio between the real power (P in kW) and apparent power (S in kVA) drawn by an electrical load. The reactive power (Q in kVAr)...

UPS - Uninterruptible Power Supply

A UPS is an uninterruptible power supply.  It is a device which maintains a continuous supply of electrical power, even in the event of failure of the...

Our website uses cookies so that we can provide a better experience.
To learn more about what cookies are and how to manage them visit AboutCookies.org