Multifunction Meter Three Phase Problem

I have the one of the different scenario, (Three phase system)
In ION 6200 Multifunction meter ,
The phase currents in the individual phases are 33.7A, 43.6A, and 56.3A
The Phase voltage is 245.7 ,247,247
The Line to Line voltage is 426 .8 ,429 and 427V
The individual phase powers are 5 kW,6.9 kW and 10.7kW
Individual Phase Power factor 0.62, 0.69 and 0.68

The Multifunction meter reads

V average = 428V
I average =45A
Power factor = 0.994
kVA (Apparent power) = 22.8 KVA
KW = 22.8 KW

If I verify the above power readings with the help V ave , I ave, PF

Power = 1.732 x 428 x 45 x 0.994 = 33.158 KW which is not matching the meter indicated reading of 22.8 KW.

Moreover the summation of individual powers of each phase ( 5 + 6.9 + 10.7) is same as the power indicated in the meter. wherein the actual calculated power as shown above is not in line with the meter reading.

Can any one help me to know the exact calculation.

Regards 
 


asked 1/13/2013
karuna2
karuna

1 Answer

It looks to me as though there may be problem with the power factor of 0.994. Can you retest this.

If you use a power factor of 0.66 (average of 0.62, 0.69, and 0.68) in your calculation, you end up with 22 kW. This is more or less the correct answer.
answered 1/14/2013 Steven McFadyen 246
Steven McFadyen

Your Answer

In order to provide an answer to this question, you must Login

I am flagging this question because...




10 inform moderator flags remaining

I am deleting this question because...




I am flagging this answer because...




10 inform moderator flags remaining

Flagging a Post

You have already flagged this post. Clicking "Remove Flag" below will remove your flag, thus reducing the count by one as well.

I am deleting this answer because...





Medium Voltage Switchgear Room Design Guide

Many medium voltage (MV) indoor switchgear rooms  exist worldwide. The complexity of these rooms varies considerably depending on location, function and...

Network Theory – Introduction and Review

In electrical engineering, Network Theory is the study of how to solve circuit problems. By analyzing circuits, the engineer looks to determine the various...

Three Phase Current - Simple Calculation

The calculation of current in a three phase system has been brought up on our site feedback and is a discussion I seem to get involved in every now and...

Railway Electrification Voltages

This post is quick introduction and overview to different railway electrification voltages used in answer to a question sent in via email. While there...

UPS Sizing - Rules of Thumb

It wasn't so long ago I was telling someone that I don't use rules of thumb as most things are easily calculated anyhow.   As it turns out I last week...

Equipment Verification (to IEC Standards)

One of the requirements to ensuring that everything works is to have equipment selected, manufactured and verified [tested] to IEC standards. Not all equipment...

Star-Delta Motor Starting - Performance

Many questions sent in to the site are in connection with motor starting and in particular star-delta.  For all but the simplest application, there is...

Induction Motor Equivalent Circuit

Induction motors are frequently used in both industrial and domestic applications.  Within the induction motor, an electrical current in the rotor is induced...

8 Motor parts and common faults

Straight forward list of some common motor faults.  If I have missed any other common faults, please take a bit of time to add them in as a comment below...

Meeting room of the future

The IET site has a video of a visit showing of a high tech meeting room developed at Napier University in Edinburgh. It a good demonstration of innovative...

Our website uses cookies so that we can provide a better experience.
To learn more about what cookies are and how to manage them visit AboutCookies.org