Outdoor Rectifier Transformer

Greeting all,

 I am working on one Light Rail Transit Maintenance Facility project. What's the different between Oil Natural Air Natural (ONAN) & Oil Force Air Force Rectifier Transformer (OFAF)? Which one is more construction cost effective (Material & installation)? Any cost difference between maintenance & operation cost in the future? Thanks a lot. 


Allan.


asked 2/8/2013
Allan Sheung2
Allan Sheung

1 Answer

Hi,

ONAN or OFAF are the type of cooling arrangements provided as primary ( ON or OF ) and secondary (AN or AF) mechanisms. If you are using forced cooling rather than natural cooling, the power rating of the transformer is enhanced. Normally forced cooling will be provided for power high capacity transformers or for critical load transformers. Retro fitting of forced cooling is also possible if same transformer needs to be retained but higher loads needs to be connected. However initial higher cost, running cost and slightly complex installation considerations needs to be set off against getting an enhanced rating output from the transformer.

Thanks

S.S. Pattabhiraman

answered 3/13/2013 Pattabhiraman 74
Pattabhiraman

Your Answer

In order to provide an answer to this question, you must Login

I am flagging this question because...




10 inform moderator flags remaining

I am deleting this question because...




I am flagging this answer because...




10 inform moderator flags remaining

Flagging a Post

You have already flagged this post. Clicking "Remove Flag" below will remove your flag, thus reducing the count by one as well.

I am deleting this answer because...





How Electrical Circuits Work

If you have no idea how electrical circuits work, or what people mean then they talk about volts and amps, hopefully I can shed a bit light.  I’m intending...

Dielectric loss in cables

Dielectrics (insulating materials for example) when subjected to a varying electric field, will have some energy loss.   The varying electric field causes...

Calculating Cable Fault Ratings

When selecting a cable, the performance of the cable under fault conditions is an important consideration. It is important that calculations be carried...

UPS - Uninterruptible Power Supply

A UPS is an uninterruptible power supply.  It is a device which maintains a continuous supply of electrical power, even in the event of failure of the...

Power Factor

Power factor is the ratio between the real power (P in kW) and apparent power (S in kVA) drawn by an electrical load. The reactive power (Q in kVAr)...

What happened to the cable notes?

If you are wondering what happened to our cable notes, the short answer is that we have moved them to myCableEngineering.com.  The "Knowledge Base" at...

Fault Calculation - Per Unit System

Per unit fault calculations is a method whereby system impedances and quantities are normalised across different voltage levels to a common base.  By removing...

How to refer fault levels across a transformer

Over the past year or so I've been involved in on going discussions related to referring fault levels from the secondary of a transformer to the primary...

RLC Circuit, Resistor Power Loss - some Modelica experiments

Modelica is an open source (free) software language for modelling complex systems. Having never used it before, I thought I would download a development...

Understanding Motor Duty Rating

One of the comments on my Motor Starting Series was asking for something on duty cycles. Here it is. As a purchaser of a motor, you have responsibility...

Our website uses cookies so that we can provide a better experience.
To learn more about what cookies are and how to manage them visit AboutCookies.org