Power for DC Motor Solution

Dear sir,

I have DC motor with specification bellow:
Power = 6Hp
Voltage = DC12V
Ampere range = 375-440A
Application = for winch
Power line that I have = 380V/3Ø/50Hz
How I must supply power for DC motor with specification above?

Thanks


asked 3/13/2013
dody_indra4
dody_indra

1 Answer

Hi,

You will have to provide 10 KVA, 3 phase, 400 volts, 50 Hz, commercially available DC 12 volt output battery charger either with battery bank of required AH capacity or direct connected to winch. Any commercial battery charger equipment manufacturer should offer the required equipment. You can also discuss with them for fine tuning the specifications.

Pattabhiraman

answered 4/19/2013 Pattabhiraman 74
Pattabhiraman

Your Answer

In order to provide an answer to this question, you must Login

I am flagging this question because...




10 inform moderator flags remaining

I am deleting this question because...




I am flagging this answer because...




10 inform moderator flags remaining

Flagging a Post

You have already flagged this post. Clicking "Remove Flag" below will remove your flag, thus reducing the count by one as well.

I am deleting this answer because...





Maxwell's Equations - Introduction

Maxwell's Equations are a set of fundamental relationships, which govern how electric and magnetic fields interact. The equations explain how these fields...

9 power supply issues solved by using a UPS

Installation of a UPS can help in reducing problems due to issues with the power supply.  A lot of people relate this to nine key issues.  Depending on...

Tech Topics/Application Notes - Siemens

There are a lot of interesting two page type notes on various medium voltage topics – switchgear, circuit breakers, bus systems etc. It is on the Siemens...

IEC 61439 Verification Methods

The (relatively new) switchgear and control gear standard, IEC 61439 'Low-voltage switchgear and controlgear assemblies' has three methods which can be...

IEC Document Designation

Often document control is dictated by project requirements, for example a particular organisation may have an existing numbering system. Existing company...

Difference Between Live and Dead Tank Circuit Breakers

A quick post in connection with an email question: Live Tank - the circuit breaker the switching unit is located in an insulator bushing which is live...

Fault Calculation - Symmetrical Components

For unbalance conditions the calculation of fault currents is more complex. One method of dealing with this is symmetrical components. Using symmetrical...

MIT OpenCourseWare

MIT OpenCourseWare, makes the materials used in teaching all MIT subjects available on the Web, free of charge, to any user in the world.

What happened to the cable notes?

If you are wondering what happened to our cable notes, the short answer is that we have moved them to myCableEngineering.com.  The "Knowledge Base" at...

Introduction to Traction Substations

Following on from my post on railway electrification voltages, I thought an introduction to traction substations would be a good idea. Traction substations...

Our website uses cookies so that we can provide a better experience.
To learn more about what cookies are and how to manage them visit AboutCookies.org