Power Factor and UPS Batteries

I will use the formula you have posted in your article, UPS Battery Sizing, but I question the use of the Power Factor being in the numerator.  If Power Factor is an expression of an inefficiency in a system, shouldn't the load on the batteries be INCREASED by way of the power factor, and thus the Power Factor would belong in the denominator in order that the batteries be sized to handle the extra load represented by this inneficiency?


asked 7/3/2013
Dwain Seppala3
Dwain Seppala

1 Answer

I would not look at power factor as an expression for efficiency.  What is really happening here, is converting VA into Watts. 

In a d.c. system real power is measure in watts and the concept of VA (volt-amps) does not exist.  Batteries are d.c. and deliver watts. 

In an a.c. system real power is measured in watts, but concept of VA now exists (due to reactive power).  UPS are normally rated in VA (or kVA).  To relate this VA to the battery capacity, it needs to be converted to watts.

If you had the rating of your UPS already in watts, then you would not need to apply the power factor. 

We have note on Power Factor, which will explain this better.

answered 7/4/2013 Steven McFadyen 246
Steven McFadyen

Your Answer

In order to provide an answer to this question, you must Login

I am flagging this question because...




10 inform moderator flags remaining

I am deleting this question because...




I am flagging this answer because...




10 inform moderator flags remaining

Flagging a Post

You have already flagged this post. Clicking "Remove Flag" below will remove your flag, thus reducing the count by one as well.

I am deleting this answer because...





What happened to the cable notes?

If you are wondering what happened to our cable notes, the short answer is that we have moved them to myCableEngineering.com.  The "Knowledge Base" at...

Equipment Verification (to IEC Standards)

One of the requirements to ensuring that everything works is to have equipment selected, manufactured and verified [tested] to IEC standards. Not all equipment...

Fault Calculation - Symmetrical Components

For unbalance conditions the calculation of fault currents is more complex. One method of dealing with this is symmetrical components. Using symmetrical...

Lighting - Lamps

Lamps are the essential part of any luminaire. These are the light generating components. Since the advent of electrical lighting in the middle of the...

Wiki Depreciation

We have had the Wiki with us for a long time now, but at last I have decided to say bye bye – more details on why below.

Lithium Ion Battery

Over recent years the Lithium Ion battery has become popular in applications requiring high power densities with small weight and footprint.  Today Lithium...

UPS Battery Sizing

Various techniques exist to enable the correct selection of batteries for UPS applications.  The procedure described below is one of the more common. ...

Lightning Protection and Earth Electrode Resistance

Most installations involve some form of lightning protection system which is connected to an earth electrode.  The function of the earth electrode is to...

8 Steps to Low Voltage Power Cable Selection and Sizing

A recurring theme on our forums is cable sizing. Now many installations are unique and require special consideration. However, a lot of the time things...

Calculating Cable Fault Ratings

When selecting a cable, the performance of the cable under fault conditions is an important consideration. It is important that calculations be carried...

Our website uses cookies so that we can provide a better experience.
To learn more about what cookies are and how to manage them visit AboutCookies.org