Power Factor and UPS Batteries

I will use the formula you have posted in your article, UPS Battery Sizing, but I question the use of the Power Factor being in the numerator.  If Power Factor is an expression of an inefficiency in a system, shouldn't the load on the batteries be INCREASED by way of the power factor, and thus the Power Factor would belong in the denominator in order that the batteries be sized to handle the extra load represented by this inneficiency?


asked 7/3/2013
Dwain Seppala3
Dwain Seppala

1 Answer

I would not look at power factor as an expression for efficiency.  What is really happening here, is converting VA into Watts. 

In a d.c. system real power is measure in watts and the concept of VA (volt-amps) does not exist.  Batteries are d.c. and deliver watts. 

In an a.c. system real power is measured in watts, but concept of VA now exists (due to reactive power).  UPS are normally rated in VA (or kVA).  To relate this VA to the battery capacity, it needs to be converted to watts.

If you had the rating of your UPS already in watts, then you would not need to apply the power factor. 

We have note on Power Factor, which will explain this better.

answered 7/4/2013 Steven McFadyen 246
Steven McFadyen

Your Answer

In order to provide an answer to this question, you must Login

I am flagging this question because...




10 inform moderator flags remaining

I am deleting this question because...




I am flagging this answer because...




10 inform moderator flags remaining

Flagging a Post

You have already flagged this post. Clicking "Remove Flag" below will remove your flag, thus reducing the count by one as well.

I am deleting this answer because...





Lithium Ion Battery

Over recent years the Lithium Ion battery has become popular in applications requiring high power densities with small weight and footprint.  Today Lithium...

Software Usage Guidelines

Using software in our  work is essential for most of us and we are becoming even more dependant on it's use.  While software is a great asset, many times...

Voltage Levels to IEC 60038

The standard aims to consolidate AC and traction voltages within the industry and defines the following bands: band 1 - A.C. systems 100 V to 1...

Mobile Phones (Brick to Implant)

The mobile phone was born in 1973. They were the size of a brick and weighed a couple of kg, making them difficult to fit into your pocket. At a few thousand...

Differential protection, the good old days

This morning I was explaining how differential protection works to a junior engineer. To give him something to read I opened up the NPAG (Network Protection...

Gas Insulated or Air Insulated Switchgear

Various arguments exist around SF6 Gas Insulated (GIS) and Air Insulated (AIS) medium voltage switchgear. Recently we had to change a GIS design to AI...

3 Phase Loads

Three phase systems are derived from three separate windings, either connected in delta or star (wye). Each winding can be treated separately, leading...

Introduction to Cathodic Protection

If two dissimilar metals are touching and an external conducting path exists, corrosion of one the metals can take place.  Moisture or other materials...

Fault Calculation - Per Unit System

Per unit fault calculations is a method whereby system impedances and quantities are normalised across different voltage levels to a common base.  By removing...

Closed Doors

"I can live with doubt and uncertainty and not knowing. I think it is much more interesting to live not knowing than to have answers that might be wrong...

Our website uses cookies so that we can provide a better experience.
To learn more about what cookies are and how to manage them visit AboutCookies.org