Transformer Maximum MVA Rating

What is the maximum and minimum MVA ratings of following transformers used in transmission and distribution of power-

1 .66KV/11KV transformers

2.132KV/11KV Transformer

  1. What is the criteria on which the manufacturers decides the MVA rating

asked 7/9/2013
ram3166
ram31

2 Answers

Voltage grade wise Transformer rating depends on Supply company rules and regulations. Highest rating of Transformer in a particular voltage grade depends on % voltage drop allowed which depends on Amperage and distance/length of line.
For Example:
I need 500MVA at 50 Km then it may not be suitable through 11/0.4KVTransformer because of the higher voltage drop being huge current. This is the way to restrict highest rating of the transformer in a particular voltage grade.
Similarly for minimum rating.
answered 9/13/2013 Er. S K Pal 2
Er. S K Pal
  • Thanks for your reply.Can you guide
    1. What is the % voltage drop allowed for EHV systems considering maximum amperage and maximum distance allowed(thumb rule based )?
    2. Also is there a restriction on Maximum MVA rating for transformers for particular voltage grades like 31.5MVA in 66KV grade,100MVA in 220KV grade,315MVA in 400KV grade. There is manual on this subject by Dakshin Haryana Bijli Vitram Nigam Ltd,India which I can mail to you. - ram31 9/29/2013

The minimum transformer is 6.6 MVA and range can be as maximum as per the application keeping in view following factors a) Voltage drop, b) Distance, c) type of conductor and d) temperature.

answered 10/28/2013 Sathya Narayana JE E/M 46
Sathya Narayana JE E/M

Your Answer

In order to provide an answer to this question, you must Login

I am flagging this question because...




10 inform moderator flags remaining

I am deleting this question because...




I am flagging this answer because...




10 inform moderator flags remaining

Flagging a Post

You have already flagged this post. Clicking "Remove Flag" below will remove your flag, thus reducing the count by one as well.

I am deleting this answer because...





Star-Delta Motor Starting - Performance

Many questions sent in to the site are in connection with motor starting and in particular star-delta.  For all but the simplest application, there is...

Windows Live Writer and myElectrical

When making adding a Note to our site we have a great online WYSIWYG editor and things are pretty simple.  However, if you prefer you can write, manage...

What does N+1 mean?

The term 'N+1' relates to redundancy and simply means that if you required 'N' items of equipment for something to work, you would have one additional...

Tech Topics/Application Notes - Siemens

There are a lot of interesting two page type notes on various medium voltage topics – switchgear, circuit breakers, bus systems etc. It is on the Siemens...

The dc resistance of conductors

This is the first of two posts on the resistance of conductors. In the next post I will look at the ac resistance, including skin effect and we deal with...

Understanding LV Circuit Breaker Fault Ratings

I think this post is going to be helpful to several of our readers. While the IEC low voltage circuit breaker Standard [IEC 60947-2, Low voltage switchgear...

UPS Sizing - Rules of Thumb

It wasn't so long ago I was telling someone that I don't use rules of thumb as most things are easily calculated anyhow.   As it turns out I last week...

What are you reading!

Reading is a bit of a hobby of mine and I"ve done a few off-topic posts in the past on this. Rather than continue doing the occasional post I thought ...

Low Voltage Fault Tables

The following tables provide quick order of magnitude fault levels for a a range of typical low voltage situations.

Capacitors - Energy Storage Application

Capacitors have numerous applications in electrical and electronic applications.  This note examines the use of capacitors to store electrical energy....

Our website uses cookies so that we can provide a better experience.
To learn more about what cookies are and how to manage them visit AboutCookies.org