Motor Voltage Drop at Starting time

Hi,

We're having a problem with a motor that has a big voltage drop (around 18%) only at the starting time. It's a 800HP motor that works with 99A and 4000V. A mechanical check has already been done on it, and everything looks fine, so the proble is related to power distribution I believe.

Any ideas?

Thank you

Motors

asked 7/29/2013
jcdelao4
jcdelao
  • It looks like the cables and switchgear are ok because the problem is only at the starting time, or what do you excatly mean by this?

    We are know doing some calculations in order to check if our current transformer is goof enough to supply our motors. Do you know how to do this?


    Tahnk you
    - jcdelao 8/5/2013

1 Answer

This answer has been selected by the question author as the best answer.

Has the voltage drop calculation been validated before ordering of cables and switchgear? Particularly for high inertia motors, you will have to factor in this input. 

Secondly your power source could be weak which is not able to support the high capacity motor starting current.

Please check and revert.

answered 7/31/2013 Pattabhiraman 74
Pattabhiraman

Your Answer

In order to provide an answer to this question, you must Login

I am flagging this question because...




10 inform moderator flags remaining

I am deleting this question because...




I am flagging this answer because...




10 inform moderator flags remaining

Flagging a Post

You have already flagged this post. Clicking "Remove Flag" below will remove your flag, thus reducing the count by one as well.

I am deleting this answer because...





Cables for MV Power Distribution - Earthed versus Unearthed Systems

Power cables can basically be classified into earthed and unearthed cables, where earthed and unearthed refer to the application for which the cable is...

UPS - Uninterruptible Power Supply

A UPS is an uninterruptible power supply.  It is a device which maintains a continuous supply of electrical power, even in the event of failure of the...

IEC 60287 Current Capacity of Cables - Rated Current

In the previous note we looked at the approach taken by the standard to the sizing of cables and illustrated this with an example.  We then looked at one...

Post Authorship

In 2011, with the introduction of it’s Panda search ranking algorithms, Google introduced tools for determining the original author of posts.  The intention...

Introduction to Cathodic Protection

If two dissimilar metals are touching and an external conducting path exists, corrosion of one the metals can take place.  Moisture or other materials...

Medium Voltage Switchgear Room Design Guide

Many medium voltage (MV) indoor switchgear rooms  exist worldwide. The complexity of these rooms varies considerably depending on location, function and...

How to Write an Electrical Note

Electrical notes are a collaborative collection of electrical engineering information and educational material. Any registered user can add content. ...

Calculating Cable Fault Ratings

When selecting a cable, the performance of the cable under fault conditions is an important consideration. It is important that calculations be carried...

IEC Document Designation

Often document control is dictated by project requirements, for example a particular organisation may have an existing numbering system. Existing company...

IEC Reference Designations

The IEC publishes a series of documents and rules governing the preparation of documents, drawings and the referencing of equipment.   Depending on country...

Our website uses cookies so that we can provide a better experience.
To learn more about what cookies are and how to manage them visit AboutCookies.org