Hi, I would like to have your opinions about voltage reduction and energy saving. There are some devices (voltage controllers)  that reduce the supplied voltage in load. Seems that it works for fluorescent lighting and for induction motors (not for those who are driven by VSD and loaded at 80%) but I would like to hear any comment referred to your knowledge or experience.

 thanks!


asked 8/22/2013
Vangelis Grivakis3
Vangelis Grivakis

2 Answers

This answer has been selected by the question author as the best answer.

I don't think this is a one shoe fits all type solution that some people say it is. 

Reducing voltage generally will reduce the power, but potentially produces other effects which may offset an gains (heaters may need to run longer, light levels may decrease requiring more fittings, torque will reduce on motors etc.).    I guess it could be useful if applied in selective situation and where the voltage is for some reason to high for the design condition.  You would also need to ensure that any device does not result in the voltage dropping below the minimum imposed by manufacturing standards.

To me, designing the electrical system itself to deliver an optimized performance would be the best way forward.  Adding a device to cater for what is perceived as an electrical system design shortfall, is not something I intuitively like.

answered 8/26/2013 Steven McFadyen 246
Steven McFadyen
I have heard it works on lighting.
answered 9/1/2013 EE65 19
EE65

Your Answer

In order to provide an answer to this question, you must Login

I am flagging this question because...




10 inform moderator flags remaining

I am deleting this question because...




I am flagging this answer because...




10 inform moderator flags remaining

Flagging a Post

You have already flagged this post. Clicking "Remove Flag" below will remove your flag, thus reducing the count by one as well.

I am deleting this answer because...





What are you reading!

Reading is a bit of a hobby of mine and I"ve done a few off-topic posts in the past on this. Rather than continue doing the occasional post I thought ...

Arc Flash Calculations

Working in the vicinity of electrical equipment poses an hazard. In addition to electric shock hazard, fault currents passing through air causes Arc Flash...

Generator Sizing & Operation Limits

When selecting a generator, there are inherent limits on the active and reactive power which can be delivered. Generators are normally sized for a certain...

Introduction to Current Transformers

Current transformers (CTs) are used to convert high level currents to a smaller more reasonable level for use as inputs to protection relays and metering...

Restricted Earth Fault Protection

The windings of many medium and small sized transformers are protected by restricted earth fault (REF) systems. The illustration shows the principal of...

Lead Acid Batteries

Lead acid batteries are cost effect and reliable, making them suitable for many applications.This note examines topics of interest associated with the...

Paternoster Lifts

These lifts were first built in 1884 by J. E. Hall and called a paternoster ("Our Father", the first two words of the Lord's Prayer in Latin) due to its...

IEC 60287 Current Capacity of Cables - An Introduction

IEC 60287 "Calculation of the continuous current rating of cables (100% load factor)" is the International Standard which defines the procedures and equations...

Voltage Levels – Confused?

I was having a conversation the other day about voltage levels.  While everyone was in agreement that low voltage was 1000 V and less, there was more confusion...

Induction Motor Equivalent Circuit

Induction motors are frequently used in both industrial and domestic applications.  Within the induction motor, an electrical current in the rotor is induced...

Our website uses cookies so that we can provide a better experience.
To learn more about what cookies are and how to manage them visit AboutCookies.org