11 kV Cable

I have a circuit in which the the transformer is of rating

 - 11kV / 415V, 50Hz, 1600kVA, Dyn11, 5% impedance connected to a 12kV, 50Hz ,630A indoor VCB with a 3cx70mm² 11kV cable.

The short circuit breaking current (AC RMS) rating of VCB is 31.5kA for 3 second.What should be the short current rating and time duration  of the 11kV cable ?


asked 12/23/2013
ram3166
ram31

1 Answer

http://www.engineering.schneider-electric.se/Attachments/ed/guide/06_determining_conductor_cross_sectional_areas.pdf

 

This link will be helpful for you. Page 544 is the right one for your question and equation is from IEC standard. Now, your question is a little bit unclear because time duration and current withstand capacity of cable are in direct proportion so usually u have to first take in consideration time for withstanding and than u will get current value and vise versa. Just read the document and if u have any question, don't hesitate to ask.

answered 12/23/2013 Mirko Lezajic 8
Mirko Lezajic

Your Answer

In order to provide an answer to this question, you must Login

I am flagging this question because...




10 inform moderator flags remaining

I am deleting this question because...




I am flagging this answer because...




10 inform moderator flags remaining

Flagging a Post

You have already flagged this post. Clicking "Remove Flag" below will remove your flag, thus reducing the count by one as well.

I am deleting this answer because...





Induction Motor Calculator

Just added a page to the tools, which will allow you to calculate the synchronous speed, slip and rated torque for an induction motor. Not a particularly...

RLC Circuit, Resistor Power Loss - some Modelica experiments

Modelica is an open source (free) software language for modelling complex systems. Having never used it before, I thought I would download a development...

Battery Sizing

This article gives an introduction to IEEE 485 method for the selection and calculation of battery capacity.

Magicians of Engineering

The other day I was reading 'Night of the New Magicians' by Mary Pope Osborn with my son.  The story is about a young boy and girl who travel back in time...

Why a Sine Wave?

I received this question by email a few weeks. First thoughts was that it is a product of the mathematics of rotating a straight conductor in a magnetic...

Welcome back Bottle

‘Kept looking at a card, y’see? Kept looking at it. Welcome back Bottle. Gods below welcome home. The Crippled God A Tale of the Malazan Book of the...

Voltage Levels to IEC 60038

The standard aims to consolidate AC and traction voltages within the industry and defines the following bands: band 1 - A.C. systems 100 V to 1...

Fault Calculations - Typical Equipment Parameters

A frequent problem in fault calculations is the obtaining of equipment parameters.  While it is always preferable to use the actual parameters of the equipment...

IEC 60287 Current Capacity of Cables - An Introduction

IEC 60287 "Calculation of the continuous current rating of cables (100% load factor)" is the International Standard which defines the procedures and equations...

Understanding Circuit Breaker Markings

IEC 60947 is the circuit breaker standard and covers the marking of breakers in detail. Any manufacturer following this standard should comply with the...

Our website uses cookies so that we can provide a better experience.
To learn more about what cookies are and how to manage them visit AboutCookies.org