Motor Starting Current and Transformer Size

Dear

I have 2 motors of 35KW and 2HP.  There is another electrical linear load of 400KW. Kindly guide me what current will draw when the motor starts and cable size as distance is 40m. 

Kindly also guide me what size of transformer is required? 

Please explain with calculation.

Kind Regards,
Haroon

Motors

asked 2/10/2014
Haroon2
Haroon
  • 1. Starting current will depend on the type of start (DOL,S/D.soft starter) employed.
    2. Will both the motors and Linear load be started at the same time?
    3. To know the transformer size what is the voltage level of motors and linear load and what is your incoming supply to Xmer? - ram31 3/26/2014

3 Answers

cable sizing doesn't depend on starting current but fuse/cb only
answered 4/23/2014 naban 6
naban
  • cable size will depend
    1 .Load current(current required by device which it is connected)
    2. type of installation(air,underground,duct)
    3. Ambient temperature
    4.Grouping factors
    5. voltage drops as per local regulations
    6 .Short circuit current capacity Adiabatic equation) - ram31 4/27/2014

Dear friend

U have a total connected load of 437 KW, first u have to decided what type of starter do u have for the motor load because a) DOL starter for lesser than 13HP the starting current is 7XFLC with good torque (b) Star Delta Starter 13HP to 48 HP starting current is 3XFLC with poor torque (c) Auto TC greater than 48HP is 4XFLC with average torque and (d) VSD starting current is 0.5 to 1.5XFLC with excellent torque, so keeping in view of above facts it seems to install 750KVA transformer
Cable sizing should be 3 times of FLC
Fuse should be 125% of the FLC
answered 4/2/2014 Sathya Narayana JE E/M 46
Sathya Narayana JE E/M
Provide the following details to provide answer-
. Type of start employed for motors 2. Will both the motors and linear load start at same time? 3. What is the voltage level,frequency of motors and linear load? 4. What is the incoming supply to Xmer?
answered 3/26/2014 ram31 66
ram31

Your Answer

In order to provide an answer to this question, you must Login

I am flagging this question because...




10 inform moderator flags remaining

I am deleting this question because...




I am flagging this answer because...




10 inform moderator flags remaining

Flagging a Post

You have already flagged this post. Clicking "Remove Flag" below will remove your flag, thus reducing the count by one as well.

I am deleting this answer because...





3 Phase Loads

Three phase systems are derived from three separate windings, either connected in delta or star (wye). Each winding can be treated separately, leading...

Microsoft OneNote

A couple of months ago I came Microsoft's OneNote and downloaded the 60 day free trail. Since then I have been using it regularly and now have a full license...

Fault Calculations - Introduction

Fault calculations are one of the most common types of calculation carried out during the design and analysis of electrical systems. These calculations...

What are you reading!

Reading is a bit of a hobby of mine and I"ve done a few off-topic posts in the past on this. Rather than continue doing the occasional post I thought ...

Periodic Electrical Installation Inspection – How Often?

How often installations are inspected is up to the owner of the installation, provided such durations do not exceed any regulatory maximums in force. ...

Dielectric loss in cables

Dielectrics (insulating materials for example) when subjected to a varying electric field, will have some energy loss.   The varying electric field causes...

Famous Scientists

Here’s list of some famous scientists. Deliberately short, with the aim to provide a quick memory jog or overview. If your looking for more detailed information...

Back to Basics - Ohm’s Law

Electrical engineering has a multitude of laws and theorems. It is fair to say the Ohm's Law is one of the more widely known; it not the most known. Developed...

Cable Trumps

Bored at work and would rather be playing trump card game with you son. The next best thing (or not) maybe the online cable trump card game from AEI Cables...

How D.C. to A.C. Inverters Work

Traditionally generation of electricity has involved rotating machines to produce alternating sinusoidal voltage and current (a.c. systems). With the development...

Our website uses cookies so that we can provide a better experience.
To learn more about what cookies are and how to manage them visit AboutCookies.org