I have a central power distribution panel (PDP) on my farm being fed with a 25KVA 7200/240v transformer by my utility supplier. I recently provided power to a new remote building (1200ft away) by using two 7200/240v 50KVA transformers. The first is fed with a 200a breaker using 20' of 4/0 alum 240v at the PDP stepping up the voltage to 7200V (center tap is not used). Then 1200' of 1/0 15K wire is buried to the second transformer where the voltage is dropped back down to 240V and feeds a 200a panel through 80' of 4/0 alum direct bury (Everything works perfectly). My question is this. Have I affected my fault current at my central PDP by this?
asked 12/23/2014
Tim2
Tim

2 Answers

Yes, you have effected it.

answered 2/3/2015 koti 2
koti

From reading your description, I don't believe you would have affected the fault level at the PDP.  The fault level is mainly a function of the upstream system, not the downstream (which is what you have changed). 

You may need to look at how the protective devices are working to satisfy yourself that there are no issues. 

answered 1/9/2015 Steven McFadyen 246
Steven McFadyen

Your Answer

In order to provide an answer to this question, you must Login

I am flagging this question because...




10 inform moderator flags remaining

I am deleting this question because...




I am flagging this answer because...




10 inform moderator flags remaining

Flagging a Post

You have already flagged this post. Clicking "Remove Flag" below will remove your flag, thus reducing the count by one as well.

I am deleting this answer because...





Voltage Drop in Installations - Concepts

Problems on achieving maximum voltage drop within an installation come up often. Depending where you live, local regulations will have different limits...

Switchboard - Forms of Internal Separation

IEC 61439 'Low-voltage switchgear and controlgear assemblies', specifies standard arrangements of switchboard (call forms of internal separation). The...

Three Phase Current - Simple Calculation

The calculation of current in a three phase system has been brought up on our site feedback and is a discussion I seem to get involved in every now and...

Robots - Interesting Videos

The robot folding towels post below was interesting enough at the time to post a link.  Recently I’ve come across a couple of other interesting videos...

Occam's Razor

I was reminded of Occam's Razor while reading a book. It's quite a simple principal of logic which has stood the test of time and is accepted as central...

Understanding LV Circuit Breaker Fault Ratings

I think this post is going to be helpful to several of our readers. While the IEC low voltage circuit breaker Standard [IEC 60947-2, Low voltage switchgear...

Battery Sizing

This article gives an introduction to IEEE 485 method for the selection and calculation of battery capacity.

Always Use PPE

A lot of our members work in countries where PPE (personal protective equipment) is regulated or they work for companies/organizations which take employee...

Three Phase Power Simplified

A single phase system is perhaps the most common type of system most people are familiar with. This is what people have in their homes and what appliances...

Are We Losing Professional Integrity

I have been thinking recently that there appears to be less professional integrity around than when I first started my career in electrical engineering...

Our website uses cookies so that we can provide a better experience.
To learn more about what cookies are and how to manage them visit AboutCookies.org