Fault Current

I have a central power distribution panel (PDP) on my farm being fed with a 25KVA 7200/240v transformer by my utility supplier. I recently provided power to a new remote building (1200ft away) by using two 7200/240v 50KVA transformers. The first is fed with a 200a breaker using 20' of 4/0 alum 240v at the PDP stepping up the voltage to 7200V (center tap is not used). Then 1200' of 1/0 15K wire is buried to the second transformer where the voltage is dropped back down to 240V and feeds a 200a panel through 80' of 4/0 alum direct bury (Everything works perfectly). My question is this. Have I affected my fault current at my central PDP by this?
asked 12/23/2014
Tim2
Tim

2 Answers

Yes, you have effected it.

answered 2/3/2015 koti 2
koti

From reading your description, I don't believe you would have affected the fault level at the PDP.  The fault level is mainly a function of the upstream system, not the downstream (which is what you have changed). 

You may need to look at how the protective devices are working to satisfy yourself that there are no issues. 

answered 1/9/2015 Steven McFadyen 246
Steven McFadyen

Your Answer

In order to provide an answer to this question, you must Login

I am flagging this question because...




10 inform moderator flags remaining

I am deleting this question because...




I am flagging this answer because...




10 inform moderator flags remaining

Flagging a Post

You have already flagged this post. Clicking "Remove Flag" below will remove your flag, thus reducing the count by one as well.

I am deleting this answer because...





Welcome back Bottle

‘Kept looking at a card, y’see? Kept looking at it. Welcome back Bottle. Gods below welcome home. The Crippled God A Tale of the Malazan Book of the...

9 power supply issues solved by using a UPS

Installation of a UPS can help in reducing problems due to issues with the power supply.  A lot of people relate this to nine key issues.  Depending on...

Three Phase Current - Simple Calculation

The calculation of current in a three phase system has been brought up on our site feedback and is a discussion I seem to get involved in every now and...

Battery Cars A to Z

Battery powered cars are a hot topic and widely debated. The pros, cons, issues and time frames can be talked about endlessly. An article by the Telegraph...

Maxwell's Equations - Introduction

Maxwell's Equations are a set of fundamental relationships, which govern how electric and magnetic fields interact. The equations explain how these fields...

Autonomous Vehicle Challenge

Two driverless and solar power vans have departed from Italy on their way to China via the silk road. During the 13,000 kM trip the vans will drive themselves...

Frame Leakage Protection

While not as popular as it once was, frame leakage protection does still have some use in some circumstances.  In essence frame leakage is an earth fault...

Cable Trumps

Bored at work and would rather be playing trump card game with you son. The next best thing (or not) maybe the online cable trump card game from AEI Cables...

Michael Faraday (the father of electrical engineering)

Famed English chemist and physicist Michael Faraday was born on September 22, 1791, in Newington Butts, a suburb of Surrey just south of the London Bridge...

The dc resistance of conductors

This is the first of two posts on the resistance of conductors. In the next post I will look at the ac resistance, including skin effect and we deal with...

Our website uses cookies so that we can provide a better experience.
To learn more about what cookies are and how to manage them visit AboutCookies.org