Fault Current

I have a central power distribution panel (PDP) on my farm being fed with a 25KVA 7200/240v transformer by my utility supplier. I recently provided power to a new remote building (1200ft away) by using two 7200/240v 50KVA transformers. The first is fed with a 200a breaker using 20' of 4/0 alum 240v at the PDP stepping up the voltage to 7200V (center tap is not used). Then 1200' of 1/0 15K wire is buried to the second transformer where the voltage is dropped back down to 240V and feeds a 200a panel through 80' of 4/0 alum direct bury (Everything works perfectly). My question is this. Have I affected my fault current at my central PDP by this?
asked 12/23/2014
Tim2
Tim

2 Answers

Yes, you have effected it.

answered 2/3/2015 koti 2
koti

From reading your description, I don't believe you would have affected the fault level at the PDP.  The fault level is mainly a function of the upstream system, not the downstream (which is what you have changed). 

You may need to look at how the protective devices are working to satisfy yourself that there are no issues. 

answered 1/9/2015 Steven McFadyen 246
Steven McFadyen

Your Answer

In order to provide an answer to this question, you must Login

I am flagging this question because...




10 inform moderator flags remaining

I am deleting this question because...




I am flagging this answer because...




10 inform moderator flags remaining

Flagging a Post

You have already flagged this post. Clicking "Remove Flag" below will remove your flag, thus reducing the count by one as well.

I am deleting this answer because...





Batteries

A battery consists of one or more cells, each of which use stored chemical energy to produce electrical energy, There are many types of cells and these...

Cable Trumps

Bored at work and would rather be playing trump card game with you son. The next best thing (or not) maybe the online cable trump card game from AEI Cables...

Questions - Reputation and Privilege

Our question and answer system while letting you do exactly what it says, is much more.  It is a dynamic user driven system, where our users not only ask...

UPS Sizing - Rules of Thumb

It wasn't so long ago I was telling someone that I don't use rules of thumb as most things are easily calculated anyhow.   As it turns out I last week...

Restricted Earth Fault Protection

The windings of many medium and small sized transformers are protected by restricted earth fault (REF) systems. The illustration shows the principal of...

Copyright Infringement

myElectrical does not support or promote the use of copyrighted material without the copyright owner's consent. If you believe that material for which...

GE's Shingijutsu Factory

GE's latest thinking on product manufacturing is he Shingijutsu philosophy or Lean production system. They have started applying this at the Louisville...

Motor Insulation

Insulation on a motor prevents interconnection of windings and the winding to earth.  When looking at motors, it is important to understand how the insulation...

ANSI (IEEE) Protective Device Numbering

The widely used United Sates standard ANSI/IEEE C37.2 'Electrical Power System Device Function Numbers, Acronyms, and Contact Designations' deals with...

Autonomous Vehicle Challenge

Two driverless and solar power vans have departed from Italy on their way to China via the silk road. During the 13,000 kM trip the vans will drive themselves...

Our website uses cookies so that we can provide a better experience.
To learn more about what cookies are and how to manage them visit AboutCookies.org