Fault Current

I have a central power distribution panel (PDP) on my farm being fed with a 25KVA 7200/240v transformer by my utility supplier. I recently provided power to a new remote building (1200ft away) by using two 7200/240v 50KVA transformers. The first is fed with a 200a breaker using 20' of 4/0 alum 240v at the PDP stepping up the voltage to 7200V (center tap is not used). Then 1200' of 1/0 15K wire is buried to the second transformer where the voltage is dropped back down to 240V and feeds a 200a panel through 80' of 4/0 alum direct bury (Everything works perfectly). My question is this. Have I affected my fault current at my central PDP by this?
asked 12/23/2014
Tim2
Tim

2 Answers

From reading your description, I don't believe you would have affected the fault level at the PDP.  The fault level is mainly a function of the upstream system, not the downstream (which is what you have changed). 

You may need to look at how the protective devices are working to satisfy yourself that there are no issues. 

answered 1/9/2015 Steven McFadyen 246
Steven McFadyen

Yes, you have effected it.

answered 2/3/2015 koti 2
koti

Your Answer

In order to provide an answer to this question, you must Login

I am flagging this question because...




10 inform moderator flags remaining

I am deleting this question because...




I am flagging this answer because...




10 inform moderator flags remaining

Flagging a Post

You have already flagged this post. Clicking "Remove Flag" below will remove your flag, thus reducing the count by one as well.

I am deleting this answer because...





MIT OpenCourseWare

MIT OpenCourseWare, makes the materials used in teaching all MIT subjects available on the Web, free of charge, to any user in the world.

Tech Topics/Application Notes - Siemens

There are a lot of interesting two page type notes on various medium voltage topics – switchgear, circuit breakers, bus systems etc. It is on the Siemens...

Lighting Design - An Introduction

From the earliest times, humans have found ways to create light. Pre-historic peoples used natural materials (moss, grass, etc.) soaked in animal fat and...

Understanding Circuit Breaker Markings

IEC 60947 is the circuit breaker standard and covers the marking of breakers in detail. Any manufacturer following this standard should comply with the...

Low Voltage Switchroom Design Guide

Low voltage (LV) switchrooms are common across all industries and one of the more common spatial requirements which need to be designed into a project...

International System of Units (SI System)

The International System of Units (abbreviated SI) is the world's most widely used system of units.  The system consists of a set of units and prefixes...

How to Check a Circuit is Dead

If you want to check a circuit is dead (not live), you should always use the three point method. First check a known live circuit, then check the dead...

Load Flow Study – how they work

A load flow study is the analysis of an electrical network carried out by an electrical engineer. The purpose is to understand how power flows around...

IEC 60287 Current Capacity of Cables - Rated Current

In the previous note we looked at the approach taken by the standard to the sizing of cables and illustrated this with an example.  We then looked at one...

Laplace Transform

Laplace transforms and their inverse are a mathematical technique which allows us to solve differential equations, by primarily using algebraic methods...

Our website uses cookies so that we can provide a better experience.
To learn more about what cookies are and how to manage them visit AboutCookies.org