Change motor direction on Star Delta and Power Factor Capacitor Bank

Dear Sirs,
I have 2 question about electrical problem.
1. We have 30kwx2 which must running at the same time, we control use star delta starter, we tried to start but one of them was wrong direction, we tried one by one by change the phase line it was R S T ( Red, Yellow, Blue) , we exchange the line Yellow to Blue under the main breaker of star delta, we started , during star mode was OK, but when change to delta suddenly tripped of breaker, and delta contactor and start failured. only the main contactor is ok. we check the motor winding by megger are OK. So, what is the correct way to change motor direction by exchange main line incoming?

2. We installed cap bank 6x5Kvar for 23kva of power electricity. the automatic is running ok, but why there is no any power factor improvement although the 6 capacitors has been charged( closed). What should we check to find out the solution. due to low power the Goverment Electricity company provide transformer 20kv-380v some where ( 200mtr) from the main breaker incoming which is connected and distributed to the our small plant . Is it influence to the capacitor bank? due to on the automatic power correction factor showing under compensation.

Thank you very much for the answer and explanation.

Best Regards,

Achmad Muklis
am_id@yahoo.com
https://id.linkedin.com/in/achmadmuklis
whats app: +6282142224747
asked 1/3/2017
Achmad Muklis2
Achmad Muklis
  • Achmad,

    Difficult questions to answer without being able to do some investigations.

    For you star-delta, the following post may help guide you in some things to look for:
    http://myelectrical.com/notes/entryid/253/star-delta-motor-staring-performance

    On the pf corrections, again difficult. Is the pf correction fully commissioning and operating as it should. Is the measurement of pf correct? Have you tried manually switching the capacitors and seeing the effect on the pf?

    Steven

    - Steven McFadyen 1/5/2017

0 Answers

Your Answer

In order to provide an answer to this question, you must Login

I am flagging this question because...




10 inform moderator flags remaining

I am deleting this question because...




I am flagging this answer because...




10 inform moderator flags remaining

Flagging a Post

You have already flagged this post. Clicking "Remove Flag" below will remove your flag, thus reducing the count by one as well.

I am deleting this answer because...





Introduction to Cathodic Protection

If two dissimilar metals are touching and an external conducting path exists, corrosion of one the metals can take place.  Moisture or other materials...

Gas Insulated or Air Insulated Switchgear

Various arguments exist around SF6 Gas Insulated (GIS) and Air Insulated (AIS) medium voltage switchgear. Recently we had to change a GIS design to AI...

Maximum Demand for Buildings

Estimating maximum demand is a topic frequently discussed. Working out how much power to allow for a building can be very subjective . Allowing too much...

LED Replacement Light Bulb

The inventor of the first visible light-emitting diode makes history again this year as it begins to show customers a 40-watt replacement GE Energy Smart...

What happened to the cable notes?

If you are wondering what happened to our cable notes, the short answer is that we have moved them to myCableEngineering.com.  The "Knowledge Base" at...

New Mail Chimp

We've been sending out Newsletters on a regular basis for a few weeks now. To do this we have been using Google's Feedburner service. While Feedburner...

IEC 60287 Current Capacity of Cables - Rated Current

In the previous note we looked at the approach taken by the standard to the sizing of cables and illustrated this with an example.  We then looked at one...

8 Motor parts and common faults

Straight forward list of some common motor faults.  If I have missed any other common faults, please take a bit of time to add them in as a comment below...

Operational Amplifier

The fundamental component of any analogue computer is the operational amplifier, or op amp. An operational amplifier (often called an op-amp,) is a high...

Lightning Risk Assessment (IEC 62305)

IEC 62305 'Protection against lightning' requires a risk assessment be carried out to determine the characteristics of any lightning protection system...

Our website uses cookies so that we can provide a better experience.
To learn more about what cookies are and how to manage them visit AboutCookies.org