Neutral Monitoring Relay for NGR

In one of my projects we were feeding the entire plant by means of 3MVA, 6.6kV,Dyn11 Transformer. This Transformer is Resistor Grounded ie., Neutral Grounding Resistor (NGR)for which a we have provided Netural Monitoring Relay (NMR). Inside the NMR there is a sensing Resistor which is of rating 5kV, if we change the rating of sensing resistor to 15kV is there any problem w.r.t operation of the NMR. Please guide me in this regards.
Neutral Earthing

asked 12/12/2011
Keshavanarayana.G3
Keshavanarayana.G

2 Answers

Thank you Sir.
answered 12/16/2011 Keshavanarayana.G 3
Keshavanarayana.G
I don’t believe there would be an issue with the voltage. The resistance needs to be the same as the NMR will be measuring the circuit through the sensing resistor and NGR. Given the voltage level, I would also confirm this with the NMR manufacturer just to be on the safe side.
answered 12/15/2011 Steven McFadyen 246
Steven McFadyen

Your Answer

In order to provide an answer to this question, you must Login

I am flagging this question because...




10 inform moderator flags remaining

I am deleting this question because...




I am flagging this answer because...




10 inform moderator flags remaining

Flagging a Post

You have already flagged this post. Clicking "Remove Flag" below will remove your flag, thus reducing the count by one as well.

I am deleting this answer because...





Large Hadron Collider

The 27 km, Euro 6 billion  Collider lies on the border between France and Switzerland, took nearly 30 years to complete.  Some of the lofty goals for the...

What are you reading!

Reading is a bit of a hobby of mine and I"ve done a few off-topic posts in the past on this. Rather than continue doing the occasional post I thought ...

Low Voltage Fault Tables

The following tables provide quick order of magnitude fault levels for a a range of typical low voltage situations.

Dielectric loss in cables

Dielectrics (insulating materials for example) when subjected to a varying electric field, will have some energy loss.   The varying electric field causes...

Understanding Motor Duty Rating

One of the comments on my Motor Starting Series was asking for something on duty cycles. Here it is. As a purchaser of a motor, you have responsibility...

Random Numbers

Using laser optical pulses the random number generator utilizes the time between arrival of random photos to generate the numbers, ensuring true accuracy...

Thermoplastic and Thermosetting Insulation

While there are a vast array of cable insulation materials, these are often divided into two general types; Thermoplastic or Thermosetting. For example...

Operational Amplifier

The fundamental component of any analogue computer is the operational amplifier, or op amp. An operational amplifier (often called an op-amp,) is a high...

HTML Symbol Entities

HTML supports a variety of entity symbols which can be entered using either numbers or an entity name.  The number or name is preceded by the ‘&’ sign...

IEC 61439 - The Switchgear Standard

The new standard IEC 61439 replaces the old 60439. Compared to the old standard, the new 61439 is a more clearly defined and takes into account the assembly...

Our website uses cookies so that we can provide a better experience.
To learn more about what cookies are and how to manage them visit AboutCookies.org