Cable sizing grouping factor by number of circuits

Dear Sir,

In direct burial installation of cable,

I found Grouping factor for number of circuit is limited by 6 circuit in your calculation tool.

More than 6 circuit does not impact any more on the grouping factor.

Could you give me detail reasons why maximum 6 circuits are only applicable for the derating? I remember IEC, ERA has derating factor upto 20 circuits.

Thanks in advance.


asked 11/30/2017
고성윤3
고성윤

4 Answers


answered 12/12/2017 Todd Peters 3
Todd Peters
edited 12/12/2017
Todd Peters3
Todd Peters

The derating factor is in line with table 4C2.  This table only goes up to six circuits (with a maximum derating factor of 0.55 in your case).  In the tool for all conditions, we allow up to 20 circuits for all installation conditions.  For any number of circuits above 6, will use the maximum derating factor, which is for 6 circuits.  Hope this makes sense.

Other derating tables do have more than six (with the maximum being 20).

Please also note that we are not supporting this particular tool going forward.  It has been superseded by our cable sizing application,  myCableEngineering.com.  I would suggest you give this a go, as you have more options and it is far easier to try out different scenarios. 

 

 

answered 12/7/2017 Steven McFadyen 246
Steven McFadyen

Thanks for your quick reply and please find two(2) captured screens below.

One is calculated with circuits 6 no and the other with circuits 20 no, and expected different groupinf factors.

However, calculation result was same with grouping fator with 0.55.

Please let me understand why grouping factor does not change although the circuit numbers are increased.

 

answered 12/7/2017 고성윤 3
고성윤

I am seeing up to 20 circuits on the cable tool.   Could you post a screenshot for me to look at (there is an insert media button, in the middle of the editor top bar)?  I can then look at the issue.

In addition to the calculation tool on myElectrical.com, which is BS 7671 if you are interested in ERA you could also look at myCableEngineering.com.  Here you can do both BS 7671 and ERA 69-30. Additionally, you have better cable management,  installation options, reporting and your cables are saved. 

 

 

answered 11/30/2017 Steven McFadyen 246
Steven McFadyen
  • Thanks for quick reply and added question with screeen capthres. - 고성윤 12/7/2017

Your Answer

In order to provide an answer to this question, you must Login

I am flagging this question because...




10 inform moderator flags remaining

I am deleting this question because...




I am flagging this answer because...




10 inform moderator flags remaining

Flagging a Post

You have already flagged this post. Clicking "Remove Flag" below will remove your flag, thus reducing the count by one as well.

I am deleting this answer because...





Famous Scientists

Here’s list of some famous scientists. Deliberately short, with the aim to provide a quick memory jog or overview. If your looking for more detailed information...

Why a Sine Wave?

I received this question by email a few weeks. First thoughts was that it is a product of the mathematics of rotating a straight conductor in a magnetic...

Why is electricity so hard to understand?

It's been a busy few months on different projects or busy couple of decades depending on how I look at it. I can say that on the odd (frequent) occasion...

Star-Delta Motor Starting - Performance

Many questions sent in to the site are in connection with motor starting and in particular star-delta.  For all but the simplest application, there is...

Robotics - Home Innovations

We have a sister note to this (Robots - Interesting Video), in which I have posted some videos of interesting robots developed by commercial corporations...

Lead us, Warleader

Delum, who had watched all in silence, his face empty of expression, now spoke in turn. ' "Lead us, Warleader, into glory."' Reading is something I do...

Low Voltage Circuit Breakers

Circuit breakers are switching devices whose primary function is to isolate parts of an electrical distribution system in the even of abnormal conditions...

What does N+1 mean?

The term 'N+1' relates to redundancy and simply means that if you required 'N' items of equipment for something to work, you would have one additional...

Capacitors - Energy Storage Application

Capacitors have numerous applications in electrical and electronic applications.  This note examines the use of capacitors to store electrical energy....

Three Phase Current - Simple Calculation

The calculation of current in a three phase system has been brought up on our site feedback and is a discussion I seem to get involved in every now and...

Our website uses cookies so that we can provide a better experience.
To learn more about what cookies are and how to manage them visit AboutCookies.org