per unit calculation gives wrong results

I have a transformer tr with :%Ztr=21 %, Str=150MVA ,220KV/66KV /21 KV

and a reactor connected to its tertiary (21 KV) ,Z reactor =22 ohm per phase.

source impedance infinite 

On 21 kv side of TR as bases  values I took KVbase1=21 KV    MVAbase1=100 MVA

--> Zpu reactor==Z reac/Zbase2=5pu


On 220 kv side of TR  as bases  values I took  KVbase2=220 KV , MVAbase2=100 MVA  --> Z2pu TR=Ztr/Zbase1=0.14 pu

conversion to base1 gives Z1pu TR=0.14*(100/100)*(220/21)2 

                                                      Z1pu TR =15.36 pu

Z putot=5pu+15.36 pu=20.36pu-->Isc=KVAbase/(1.732*21kv*20.36pu)=135A

which is wrong because the MVA methid give 535 A. Could you help me to find the error?



asked 3/26/2018
f13tun2
f13tun
  • I found the error ,i should not convert the p.u of the transformer because it will be the same on both side of it
    so Z pu total=z pu reactor + zpu tr=5+0.14=5.14 pu on base 21 kv , 100 MVA
    so Isc=KVAbase/(1.732*21kv*5.14pu)=534.89 A
    The MVA method already gives 535 A.
    Thank you any way - f13tun 3/26/2018

0 Answers

Your Answer

In order to provide an answer to this question, you must Login

I am flagging this question because...




10 inform moderator flags remaining

I am deleting this question because...




I am flagging this answer because...




10 inform moderator flags remaining

Flagging a Post

You have already flagged this post. Clicking "Remove Flag" below will remove your flag, thus reducing the count by one as well.

I am deleting this answer because...





Lighting Design - An Introduction

From the earliest times, humans have found ways to create light. Pre-historic peoples used natural materials (moss, grass, etc.) soaked in animal fat and...

Tip – Latitude and Longitude on Large Scale Plans

If you are working on a large plan, get the real coordinates [latitude, longitude] for two or more points and add them to the drawing. That way you can...

How to Size Current Transformers

The correct sizing of current transformers is required to ensure satisfactory operation of measuring instruments and protection relays. Several methods...

Cable Sizing Tool

Our cable sizing tool is one of the more popular tools on the site.  The tool enables cables to be sized in compliance with BS 7671 (the IEE Wiring Regulations...

Earth Electrode Resistance

Earthing of electrical systems is essential for the correct functioning and the protecting of life and equipment in the event of faults.  The earth electrode...

Electrical Engineering

Electrical engineering is a field that covers a wide variety of sub-fields, including electricity and electronics. It is a field that goes back to the...

A mechanical engineering paper, some history and memories

I was digging in my bookshelf and came across the 80th Anniversary Association of Mine Resident Engineers, Papers and Discussions Commemorative Edition...

Maxwell's Equations - Gauss's Electric Field Law

Gauss's Electrical law defines the relation between charge ("Positive" & "Negative") and electric field.  The law was initially formulated by Carl Friedrich...

Periodic Electrical Installation Inspection – What to Inspect?

This is the second post in a series of two on periodic electrical inspections. In the first post, I discussed how often inspections should be carried out...

What are you reading!

Reading is a bit of a hobby of mine and I"ve done a few off-topic posts in the past on this. Rather than continue doing the occasional post I thought ...

Our website uses cookies so that we can provide a better experience.
To learn more about what cookies are and how to manage them visit AboutCookies.org