60 kW Motor genset size?

i want to start and run the motor with genset, the motor is of 60kw, 104ampere,415 voltage , 3 phase direct on line, so please send me the calculation to select the genset.
asked 12/26/2011
Engr.Naeem1
Engr.Naeem

1 Answer

You need to ensure the generator is adequate for the normal power load of the motor, starting load and that there is no excessive voltage drop during running or starting.

I just did a quick Google search and one site was recommending 100 kW (star delta starting) and 225 kW (for direct on line). Another site gave a rule of thumb of 1 kW of generator for each 0.56 to 0.75 kW of motor (80 to 107 kW for a 60 kW motor). Quite a bit of a range here.

Possibly the better way is to calculate the running kW, running kVA, staring kW and starting kVA. Compare these to figures given by the generator manufacturer on their datasheets to select the correct generator. The generator manufacturer can also probably provide some good input on the correct size to use.

Should also be careful about voltage drop. In addition to not stalling the motor, you will want to ensure that any generator control equipment connected to the same bus is not affected.
answered 1/22/2012 Steven McFadyen 246
Steven McFadyen

Your Answer

In order to provide an answer to this question, you must Login

I am flagging this question because...




10 inform moderator flags remaining

I am deleting this question because...




I am flagging this answer because...




10 inform moderator flags remaining

Flagging a Post

You have already flagged this post. Clicking "Remove Flag" below will remove your flag, thus reducing the count by one as well.

I am deleting this answer because...





Fire Resistant and Fire Retardant Cables

Fire resistant and fire retardant cable sheaths are design to resist combustion and limit the propagation of flames. Low smokes cables have a sheath designed...

Meeting room of the future

The IET site has a video of a visit showing of a high tech meeting room developed at Napier University in Edinburgh. It a good demonstration of innovative...

110 or 230 Volts

I've been considering a blog on the 110 or 230 Volt issue for a while.  While browsing the Internet I came across a great summary by Borat over at  engineering...

Differential protection, the good old days

This morning I was explaining how differential protection works to a junior engineer. To give him something to read I opened up the NPAG (Network Protection...

Motor Starting - Introduction

Motor starting and its associated problems are well-known to many people who have worked on large industrial processes. However, these things are, of course...

UPS Sizing - Rules of Thumb

It wasn't so long ago I was telling someone that I don't use rules of thumb as most things are easily calculated anyhow.   As it turns out I last week...

What are you reading!

Reading is a bit of a hobby of mine and I"ve done a few off-topic posts in the past on this. Rather than continue doing the occasional post I thought ...

A mechanical engineering paper, some history and memories

I was digging in my bookshelf and came across the 80th Anniversary Association of Mine Resident Engineers, Papers and Discussions Commemorative Edition...

Load Flow Study – how they work

A load flow study is the analysis of an electrical network carried out by an electrical engineer. The purpose is to understand how power flows around...

Inductance

When current flows within a wire, a magnetic field is created. The potion of this magnetic field perpendicular to the wire is called the magnetic flux...

Our website uses cookies so that we can provide a better experience.
To learn more about what cookies are and how to manage them visit AboutCookies.org