Transformer Impedance Calculation

Hi all, I have a very fundamental question to ask. To compute a 3 phase fault current of a circuit supplied by a 1MVA transformer 22kV/ 400V with 5% impedance without using PU method, I understand it goes:

TF impedance = 5% x 400^2/ 1x10^6 = 0.0084 ohm

The 3 phase fault current per phase = 400/ 1.732/ 0.0084= 27.5kA

I am puzzled by the TF impedance calculation.. why is there no 1.732 factor as with all 3 phase power calculations in this instance? Sorry for the very layman question asked here. But am really confused. Thanks.

 


asked 5/26/2018
Fbearn2
Fbearn

1 Answer

kVA / Voltage x 1.73 / TX Z%
1000 / 400 x 1.73 / 5% = 28,9 kA
answered 4 months ago Paddy Keys 3
Paddy Keys

Your Answer

In order to provide an answer to this question, you must Login

I am flagging this question because...




10 inform moderator flags remaining

I am deleting this question because...




I am flagging this answer because...




10 inform moderator flags remaining

Flagging a Post

You have already flagged this post. Clicking "Remove Flag" below will remove your flag, thus reducing the count by one as well.

I am deleting this answer because...





Electromechanical Relays

Electromechanical relays have been the traditional backbone of electrical protection systems.  While over recent years these have been replaced by microprocessor...

Fault Calculations - Introduction

Fault calculations are one of the most common types of calculation carried out during the design and analysis of electrical systems. These calculations...

9 power supply issues solved by using a UPS

Installation of a UPS can help in reducing problems due to issues with the power supply.  A lot of people relate this to nine key issues.  Depending on...

What happened to the cable notes?

If you are wondering what happened to our cable notes, the short answer is that we have moved them to myCableEngineering.com.  The "Knowledge Base" at...

Introduction to Current Transformers

Current transformers (CTs) are used to convert high level currents to a smaller more reasonable level for use as inputs to protection relays and metering...

Lightning Risk Assessment (IEC 62305)

IEC 62305 'Protection against lightning' requires a risk assessment be carried out to determine the characteristics of any lightning protection system...

Maximum Demand for Buildings

Estimating maximum demand is a topic frequently discussed. Working out how much power to allow for a building can be very subjective . Allowing too much...

Power Transformers - An Introduction

One of the fundamental requirements of an alternating current distribution systems it to have the ability to change the magnitude of voltages.  It is more...

UPS Battery Sizing

Various techniques exist to enable the correct selection of batteries for UPS applications.  The procedure described below is one of the more common. ...

Cables for MV Power Distribution - Earthed versus Unearthed Systems

Power cables can basically be classified into earthed and unearthed cables, where earthed and unearthed refer to the application for which the cable is...

Our website uses cookies so that we can provide a better experience.
To learn more about what cookies are and how to manage them visit AboutCookies.org