Power calculation disagreement

Good afternoon,

I tried what I thought would be simple power calculations, but the calculations are not balancing.  It seems that I'm doing something fundamentally incorrect.  Here's a hypothetical situation that illustrates the problem.

There is a new 120/208 panel that has only one 2-pole breaker installed.  The load is 208 and the neutral is not used by the load.  The panel power meter shows line currents of 10, 10, 0.  The power factor is .90.  With the above readings, I believe the power for the panel (which represents only the one load) would be:

Average of line currents * line voltage * power factor * sqrt(3)

6.67 * 208 * .9 * 1.732 = 2,162 Watts

Then I go out to the field with my multi-meter and calculate power at the load:

Line current * line voltage * power factor (assumed to be same as panel)

10 * 208 * .9 = 1,872 Watts.

Why do I calculate ~15% lower power at the load?

Thanks,

Paul


asked 6/30/2018
PBerry2
PBerry

0 Answers

Your Answer

In order to provide an answer to this question, you must Login

I am flagging this question because...




10 inform moderator flags remaining

I am deleting this question because...




I am flagging this answer because...




10 inform moderator flags remaining

Flagging a Post

You have already flagged this post. Clicking "Remove Flag" below will remove your flag, thus reducing the count by one as well.

I am deleting this answer because...





Inductance

When current flows within a wire, a magnetic field is created. The potion of this magnetic field perpendicular to the wire is called the magnetic flux...

ABB Technical Guides - Motor Operation

ABB has produced a range of technical guides that offer concise explanations of the major technologies and technical issues in low voltage AC drives. ...

Capacitor Theory

Capacitors are widely used in electrical engineering for functions such as energy storage, power factor correction, voltage compensation and many others...

How D.C. to A.C. Inverters Work

Traditionally generation of electricity has involved rotating machines to produce alternating sinusoidal voltage and current (a.c. systems). With the development...

Motor Efficiency Classification

Electric motors are one of the most widely used items of electrical equipment. Improving motor efficiency benefits include, reduced power demand, lower...

Occam's Razor

I was reminded of Occam's Razor while reading a book. It's quite a simple principal of logic which has stood the test of time and is accepted as central...

Cable Sizing Software

When sizing cables nearly, everyone uses some form of software. This ranges from homespun spreadsheets to complex network analyses software. Each has its...

Are We Losing Professional Integrity

I have been thinking recently that there appears to be less professional integrity around than when I first started my career in electrical engineering...

Battery Sizing

This article gives an introduction to IEEE 485 method for the selection and calculation of battery capacity.

Paternoster Lifts

These lifts were first built in 1884 by J. E. Hall and called a paternoster ("Our Father", the first two words of the Lord's Prayer in Latin) due to its...

Our website uses cookies so that we can provide a better experience.
To learn more about what cookies are and how to manage them visit AboutCookies.org