Power calculation disagreement

Good afternoon,

I tried what I thought would be simple power calculations, but the calculations are not balancing.  It seems that I'm doing something fundamentally incorrect.  Here's a hypothetical situation that illustrates the problem.

There is a new 120/208 panel that has only one 2-pole breaker installed.  The load is 208 and the neutral is not used by the load.  The panel power meter shows line currents of 10, 10, 0.  The power factor is .90.  With the above readings, I believe the power for the panel (which represents only the one load) would be:

Average of line currents * line voltage * power factor * sqrt(3)

6.67 * 208 * .9 * 1.732 = 2,162 Watts

Then I go out to the field with my multi-meter and calculate power at the load:

Line current * line voltage * power factor (assumed to be same as panel)

10 * 208 * .9 = 1,872 Watts.

Why do I calculate ~15% lower power at the load?

Thanks,

Paul


asked 6/30/2018
PBerry2
PBerry

0 Answers

Your Answer

In order to provide an answer to this question, you must Login

I am flagging this question because...




10 inform moderator flags remaining

I am deleting this question because...




I am flagging this answer because...




10 inform moderator flags remaining

Flagging a Post

You have already flagged this post. Clicking "Remove Flag" below will remove your flag, thus reducing the count by one as well.

I am deleting this answer because...





Electrical Engineering

Electrical engineering is a field that covers a wide variety of sub-fields, including electricity and electronics. It is a field that goes back to the...

Restricted Earth Fault Protection

The windings of many medium and small sized transformers are protected by restricted earth fault (REF) systems. The illustration shows the principal of...

RLC Circuit, Resistor Power Loss - some Modelica experiments

Modelica is an open source (free) software language for modelling complex systems. Having never used it before, I thought I would download a development...

LED Replacement Light Bulb

The inventor of the first visible light-emitting diode makes history again this year as it begins to show customers a 40-watt replacement GE Energy Smart...

Aluminium Windings - Dry Type Transformers

The other day I was talking to a colleague who is a building services consultant.  Despite regularly specifying dry-type/cast resin transformers he was...

New Mail Chimp

We've been sending out Newsletters on a regular basis for a few weeks now. To do this we have been using Google's Feedburner service. While Feedburner...

Fault Calculation - Per Unit System

Per unit fault calculations is a method whereby system impedances and quantities are normalised across different voltage levels to a common base.  By removing...

HTML Symbol Entities

HTML supports a variety of entity symbols which can be entered using either numbers or an entity name.  The number or name is preceded by the ‘&’ sign...

Mobile Phones (Brick to Implant)

The mobile phone was born in 1973. They were the size of a brick and weighed a couple of kg, making them difficult to fit into your pocket. At a few thousand...

Induction Motor Calculator

Just added a page to the tools, which will allow you to calculate the synchronous speed, slip and rated torque for an induction motor. Not a particularly...

Our website uses cookies so that we can provide a better experience.
To learn more about what cookies are and how to manage them visit AboutCookies.org