Power calculation disagreement

Good afternoon,

I tried what I thought would be simple power calculations, but the calculations are not balancing.  It seems that I'm doing something fundamentally incorrect.  Here's a hypothetical situation that illustrates the problem.

There is a new 120/208 panel that has only one 2-pole breaker installed.  The load is 208 and the neutral is not used by the load.  The panel power meter shows line currents of 10, 10, 0.  The power factor is .90.  With the above readings, I believe the power for the panel (which represents only the one load) would be:

Average of line currents * line voltage * power factor * sqrt(3)

6.67 * 208 * .9 * 1.732 = 2,162 Watts

Then I go out to the field with my multi-meter and calculate power at the load:

Line current * line voltage * power factor (assumed to be same as panel)

10 * 208 * .9 = 1,872 Watts.

Why do I calculate ~15% lower power at the load?

Thanks,

Paul


asked 6/30/2018
PBerry2
PBerry

0 Answers

Your Answer

In order to provide an answer to this question, you must Login

I am flagging this question because...




10 inform moderator flags remaining

I am deleting this question because...




I am flagging this answer because...




10 inform moderator flags remaining

Flagging a Post

You have already flagged this post. Clicking "Remove Flag" below will remove your flag, thus reducing the count by one as well.

I am deleting this answer because...





What is LED?

Light Emitting Diodes (LED ) are increasing gaining favour in both the domestic and commercial sectors; due to their efficiency, sustainability and durability...

IEC Document Designation

Often document control is dictated by project requirements, for example a particular organisation may have an existing numbering system. Existing company...

Standard Cable & Wire Sizes

IEC 60228 is the International Electrotechnical Commission's international standard on conductors of insulated cables. Among other things, it defines a...

Electromechanical Relays

Electromechanical relays have been the traditional backbone of electrical protection systems.  While over recent years these have been replaced by microprocessor...

Lead us, Warleader

Delum, who had watched all in silence, his face empty of expression, now spoke in turn. ' "Lead us, Warleader, into glory."' Reading is something I do...

Cable Sizing Tool

Our cable sizing tool is one of the more popular tools on the site.  The tool enables cables to be sized in compliance with BS 7671 (the IEE Wiring Regulations...

Surface Treatment – Ladders, Trays and Baskets

Steel ladders, trays and baskets form the backbone of cable containment systems. Often these items need some form of surface treatment to prevent corrosion...

Periodic Electrical Installation Inspection – What to Inspect?

This is the second post in a series of two on periodic electrical inspections. In the first post, I discussed how often inspections should be carried out...

Fire Resistant and Fire Retardant Cables

Fire resistant and fire retardant cable sheaths are design to resist combustion and limit the propagation of flames. Low smokes cables have a sheath designed...

Lead Acid Batteries

Lead acid batteries are cost effect and reliable, making them suitable for many applications.This note examines topics of interest associated with the...

Our website uses cookies so that we can provide a better experience.
To learn more about what cookies are and how to manage them visit AboutCookies.org