How to limit DC offset to 20% with a time delay?

"Lets say you wanted to add a time delay to the relay in order to allow the DC Component to decay before interrupting the fault.
How would you calculate it by hand?
%dc = 100e(-t/45)"

asked 3/7/2012
Mjomah6
Mjomah

6 Answers

Thank you Steven.
answered 3/15/2012 Mjomah 6
Mjomah
Mjomah I don’ think there is any ignorance. You question is investigative and forcing me to think a bit.

From your description, the time constant would be (1/2*pi*f)(X/R); at 50 Hz this would be 82.8 mS.

For the dc component, I=Ipeak*e^(-t/timeConstant); so to get to 20% we have (I’ll do this in stages):

20=100*e^(t/0.0828) -> 0.2=e^(-t/0.0828)
-> ln(0.2)=-t/0.0828 -> -1.6094=-t/0.0828
-> t=133.3 mS

If you see any problems with the above, please post and we can keep working through this till we have a good answer.

As a note, the peak dc current on which the breaker 20% is decided is likely higher than the actual fault peak current you will be seeing. If 133.3mS is too long, by modifying the method above to use both these figures, you could theoretically derive a shorter time.
answered 3/14/2012 Steven McFadyen 246
Steven McFadyen
Steven,
please excuse my ignorance, but to make sure i understand can you provide an example? Let's say for instance the a power system study was conducted and the X/R ratio at the bus was 26 (hypothetically). Let's assume that the Circuit breaker had a DC% capability of 20%. How would you show you added time delay in order for the Circuit breaker to allow enough time for the DC component to decay? (If you can show a calculation)
It's not an actual problem, but I am aware that IEC accounts for the DC component.
answered 3/13/2012 Mjomah 6
Mjomah
Here is a link to a Siemens page which tries to explain this (pretty much in line with what your saying):

http://www.energy.siemens.com/us/en/power-distribution/medium-voltage-switchgear/mvgcb.htm#content=Higher%20X%2FR%20Ratio%20

This is the standard the beakers are tested to, but in reality you may have a quicker (or slower) decay. By using actual system X/R, I think you will get a better solution to your problem.

Without knowing your problem, isn't the dc decay taken into consideration in the performance of your circuit breaker. Do you really need an external delay for this. If your problem is such that you do need this delay, my first thought would be to not include any contact parting time.
answered 3/9/2012 Steven McFadyen 246
Steven McFadyen
Steven,
thank you for the quick response and you answered the question, but i'm a little confused on when the standard gives you standard time constants. But your saying that at your fault location if the X/R ratio is greater than 17 than you would use the X/R to calculate the new time constant? Is that Correct?
If i wanted to add a time delay for before the circuit breaker would trip, would it be added with the contact parting time (t/.045) numerator.
answered 3/8/2012 Mjomah 6
Mjomah
If you looking for a 20% decay; 20% on 100 = 80. Putting this in your equation would gives 80=100e(-t/45), which you need to solve by taking the natural log of both sides and finding t. Also think 45 should be 0.045.

If I have misunderstood your question, please let me know.

The time constant of 45 ms is recommended by the standards as typical. If you know the X/R ratio you can get a more accurate estimate from time constant = (X/R)/2πf
answered 3/8/2012 Steven McFadyen 246
Steven McFadyen

Your Answer

In order to provide an answer to this question, you must Login

I am flagging this question because...




10 inform moderator flags remaining

I am deleting this question because...




I am flagging this answer because...




10 inform moderator flags remaining

Flagging a Post

You have already flagged this post. Clicking "Remove Flag" below will remove your flag, thus reducing the count by one as well.

I am deleting this answer because...





Hazardous Areas – IEC and NEC/CEC Comparison

Depending where in the world you work, you are likely following one of two standards International Electrotechnical Commission (IEC) National...

Smarter Electrical Distribution

The other day I came across an article in Technology Review on the development of a smart transformer. A professor at North Carolina State University is...

How to Write an Electrical Note

Electrical notes are a collaborative collection of electrical engineering information and educational material. Any registered user can add content. ...

110 or 230 Volts

I've been considering a blog on the 110 or 230 Volt issue for a while.  While browsing the Internet I came across a great summary by Borat over at  engineering...

The ac resistance of conductors

In a previous article I looked at the dc resistance of conductors and in this article we turn our attention to ac resistance. If you have not read the...

Fault Calculations - Introduction

Fault calculations are one of the most common types of calculation carried out during the design and analysis of electrical systems. These calculations...

What is a rectifier transformer?

I've recently come across this question a couple times browsing the internet. Decided to give a quick answer here. A rectifier transformer is a transformer...

Variable Frequency Drive

Variable frequency drives are widely used to control the speed of ac motors.  This note looks at the mechanisms which enable drive units to control the...

Voltage Drop in Installations - Concepts

Problems on achieving maximum voltage drop within an installation come up often. Depending where you live, local regulations will have different limits...

Cable Sizing Software

When sizing cables nearly, everyone uses some form of software. This ranges from homespun spreadsheets to complex network analyses software. Each has its...

Our website uses cookies so that we can provide a better experience.
To learn more about what cookies are and how to manage them visit AboutCookies.org