How to limit DC offset to 20% with a time delay?

"Lets say you wanted to add a time delay to the relay in order to allow the DC Component to decay before interrupting the fault.
How would you calculate it by hand?
%dc = 100e(-t/45)"

asked 3/7/2012
Mjomah6
Mjomah

6 Answers

Thank you Steven.
answered 3/15/2012 Mjomah 6
Mjomah
Mjomah I don’ think there is any ignorance. You question is investigative and forcing me to think a bit.

From your description, the time constant would be (1/2*pi*f)(X/R); at 50 Hz this would be 82.8 mS.

For the dc component, I=Ipeak*e^(-t/timeConstant); so to get to 20% we have (I’ll do this in stages):

20=100*e^(t/0.0828) -> 0.2=e^(-t/0.0828)
-> ln(0.2)=-t/0.0828 -> -1.6094=-t/0.0828
-> t=133.3 mS

If you see any problems with the above, please post and we can keep working through this till we have a good answer.

As a note, the peak dc current on which the breaker 20% is decided is likely higher than the actual fault peak current you will be seeing. If 133.3mS is too long, by modifying the method above to use both these figures, you could theoretically derive a shorter time.
answered 3/14/2012 Steven McFadyen 246
Steven McFadyen
Steven,
please excuse my ignorance, but to make sure i understand can you provide an example? Let's say for instance the a power system study was conducted and the X/R ratio at the bus was 26 (hypothetically). Let's assume that the Circuit breaker had a DC% capability of 20%. How would you show you added time delay in order for the Circuit breaker to allow enough time for the DC component to decay? (If you can show a calculation)
It's not an actual problem, but I am aware that IEC accounts for the DC component.
answered 3/13/2012 Mjomah 6
Mjomah
Here is a link to a Siemens page which tries to explain this (pretty much in line with what your saying):

http://www.energy.siemens.com/us/en/power-distribution/medium-voltage-switchgear/mvgcb.htm#content=Higher%20X%2FR%20Ratio%20

This is the standard the beakers are tested to, but in reality you may have a quicker (or slower) decay. By using actual system X/R, I think you will get a better solution to your problem.

Without knowing your problem, isn't the dc decay taken into consideration in the performance of your circuit breaker. Do you really need an external delay for this. If your problem is such that you do need this delay, my first thought would be to not include any contact parting time.
answered 3/9/2012 Steven McFadyen 246
Steven McFadyen
Steven,
thank you for the quick response and you answered the question, but i'm a little confused on when the standard gives you standard time constants. But your saying that at your fault location if the X/R ratio is greater than 17 than you would use the X/R to calculate the new time constant? Is that Correct?
If i wanted to add a time delay for before the circuit breaker would trip, would it be added with the contact parting time (t/.045) numerator.
answered 3/8/2012 Mjomah 6
Mjomah
If you looking for a 20% decay; 20% on 100 = 80. Putting this in your equation would gives 80=100e(-t/45), which you need to solve by taking the natural log of both sides and finding t. Also think 45 should be 0.045.

If I have misunderstood your question, please let me know.

The time constant of 45 ms is recommended by the standards as typical. If you know the X/R ratio you can get a more accurate estimate from time constant = (X/R)/2πf
answered 3/8/2012 Steven McFadyen 246
Steven McFadyen

Your Answer

In order to provide an answer to this question, you must Login

I am flagging this question because...




10 inform moderator flags remaining

I am deleting this question because...




I am flagging this answer because...




10 inform moderator flags remaining

Flagging a Post

You have already flagged this post. Clicking "Remove Flag" below will remove your flag, thus reducing the count by one as well.

I am deleting this answer because...





Getting Started with Patents

If you have a great idea or invent something the last thing you want is someone to steal the idea. One of the things you can do is protect the intellectual...

How to Size Power Cable Duct

Some colleagues had an issue earlier in the week on sizing conduits to be cast in concrete for some power cables . It became clear that none of us had...

IEC 60287 Current Capacity of Cables - An Introduction

IEC 60287 "Calculation of the continuous current rating of cables (100% load factor)" is the International Standard which defines the procedures and equations...

Fire Resistant and Fire Retardant Cables

Fire resistant and fire retardant cable sheaths are design to resist combustion and limit the propagation of flames. Low smokes cables have a sheath designed...

How Electrical Circuits Work

If you have no idea how electrical circuits work, or what people mean then they talk about volts and amps, hopefully I can shed a bit light.  I’m intending...

Differential protection, the good old days

This morning I was explaining how differential protection works to a junior engineer. To give him something to read I opened up the NPAG (Network Protection...

How to Check a Circuit is Dead

If you want to check a circuit is dead (not live), you should always use the three point method. First check a known live circuit, then check the dead...

Contribute to myElectrcial

Have an opinion or something to say, want to ask or answer questions, share your knowledge then use our site to do it . As a community of people interested...

IEC 61439 Verification Methods

The (relatively new) switchgear and control gear standard, IEC 61439 'Low-voltage switchgear and controlgear assemblies' has three methods which can be...

Aluminium Windings - Dry Type Transformers

The other day I was talking to a colleague who is a building services consultant.  Despite regularly specifying dry-type/cast resin transformers he was...

Our website uses cookies so that we can provide a better experience.
To learn more about what cookies are and how to manage them visit AboutCookies.org