Effect of voltage drop on induction motor current

"We've two motors of 75 kW and 150 kw rating which are driving centrifugal pumps. The normal running current of 75 kW motor is 115A whereas its low current security is set at 90A.
Whenever 150 kW motor cuts in, the low current security of 75 kW motor gets actuated. We've measured the voltage drop during the startup of 150 kW motor which is 15 - 20V.
My question is'
1. Whenever there is a voltage drop on an induction motor, the current should increased or decreased ?"
Motors

asked 3/15/2012
faysalnaeem1
faysalnaeem

2 Answers

The current will increase but it also depends on the starter you are using. I assume you are using a star delta starter, although the are expensive to buy you can use a soft starter or a variable speed drive.
answered 5/15/2012 Interserve 2
Interserve
As the voltage reduces the motor current will increase (but the speed and torque will decrease). Exactly what happens depends on the magnitude and duration of the dip. Limited decrease in voltages should not be a problems as long as the motor current remains below the nameplate rating. For larger voltage dips the motor may stall (or go into a starting condition), which would increase the current above normal conditions and require the protective devices to operate.

If your 20V drop is related to 400 V (just guessing), that's 5% which should not really cause problems. From your description, it may be that the overload protection is set at less than the name plate full load current. In that case you could increase it to overcome the issue.

If this control voltage is also derived from the system voltage, a drop in this may also cause the contactor to drop out.

If you have measured the voltage drop, can you also measure the current then you will know what is
answered 3/20/2012 Steven McFadyen 246
Steven McFadyen

Your Answer

In order to provide an answer to this question, you must Login

I am flagging this question because...




10 inform moderator flags remaining

I am deleting this question because...




I am flagging this answer because...




10 inform moderator flags remaining

Flagging a Post

You have already flagged this post. Clicking "Remove Flag" below will remove your flag, thus reducing the count by one as well.

I am deleting this answer because...





IEC 60287 Current Capacity of Cables - An Introduction

IEC 60287 "Calculation of the continuous current rating of cables (100% load factor)" is the International Standard which defines the procedures and equations...

How a Digital Substation Works

Traditionally substations have used circuit breakers, current transformers (CT), voltage transformers (VT) and protection relays all wired together using...

8 Steps to Low Voltage Power Cable Selection and Sizing

A recurring theme on our forums is cable sizing. Now many installations are unique and require special consideration. However, a lot of the time things...

What does N+1 mean?

The term 'N+1' relates to redundancy and simply means that if you required 'N' items of equipment for something to work, you would have one additional...

Three Phase Power Simplified

A single phase system is perhaps the most common type of system most people are familiar with. This is what people have in their homes and what appliances...

Occam's Razor

I was reminded of Occam's Razor while reading a book. It's quite a simple principal of logic which has stood the test of time and is accepted as central...

Software Usage Guidelines

Using software in our  work is essential for most of us and we are becoming even more dependant on it's use.  While software is a great asset, many times...

Why use catalogues

I'm a fan of using manufacturers catalogues. There are two main reasons for this. Firstly, if your involved in the purchase of equipment, you will likely...

IEEE Winds of Change

IEEE TV has a part series of videos on wind power and it's implication. For a really good overview to the technologies and issues around wind power, these...

Generator Sizing & Operation Limits

When selecting a generator, there are inherent limits on the active and reactive power which can be delivered. Generators are normally sized for a certain...

Our website uses cookies so that we can provide a better experience.
To learn more about what cookies are and how to manage them visit AboutCookies.org