Single phase circuit on 3 phase current calc

Hi,

I have a question regarding calculating current in a 3 phase supply. I have my head around how to calculate the current in a 3 phase circuit. For example if we have a 22kw load assuming a power factor of 0.8 would be 22000/(1.732x415x0.8) = 38.25A

However if I’m installing a 7.2kw single phase circuit on a 3-phase supply I.e using L1 (or L2 or L3) and neutral. Is the calc 7200/(1.732x230x0.8) = 18.06 amps

It’s not the usual 7200/230 (simplified calc) where the current would be 31.30A we would use for a single phase supply?. Even though it is a single phase circuit?.

Thanks,

A.

asked 6/15/2019
spark83192
spark8319

2 Answers

Hi Steven,

I have a related question.  

We often utilize 240V 3PH to supply mixed 3PH loads and 1PH 240V loads on any two phases.

I want to confirm the calculation of current in the single phase loads at the line-to-line voltage in the following simplified example where the current for a single phase load of 1kVA = (1000VA / 2) / 240V = 2.08A (as opposed to 1000VA/240V = 4.17A).  The resulting system would then have a balanced 3PH load of approximately 9A.

 


Thanks.

 

answered 10/23/2019 tnhokie27 2
tnhokie27
edited 10/23/2019
tnhokie272
tnhokie27

Looks like in your first example you are using 415 V, and 230 in your second.  The common convention is 415/240 or 400/230 V  [line-line/line-neutral].

This is how I like to calculate:

First example: 22000/0.8 = 27500 VA.  I =  (27500/3) / 240 = 38.2.  Same as your answer, just a slightly different way of calculating (and using 240 V, whereas 415/1.732 = 239.6 more accurately).  

Second example: 7200/0.8 = 90000VA = I = 9000/230 = 39.1 A.  

In your formulae using 1.732 x voltage assumes the voltage is line-line.  In the second example, the voltage is line-neutral. 

Hope this helps.

answered 6/16/2019 Steven McFadyen 246
Steven McFadyen

Your Answer

In order to provide an answer to this question, you must Login

I am flagging this question because...




10 inform moderator flags remaining

I am deleting this question because...




I am flagging this answer because...




10 inform moderator flags remaining

Flagging a Post

You have already flagged this post. Clicking "Remove Flag" below will remove your flag, thus reducing the count by one as well.

I am deleting this answer because...





Maxwell's Equations - Gauss's Electric Field Law

Gauss's Electrical law defines the relation between charge ("Positive" & "Negative") and electric field.  The law was initially formulated by Carl Friedrich...

Why use catalogues

I'm a fan of using manufacturers catalogues. There are two main reasons for this. Firstly, if your involved in the purchase of equipment, you will likely...

Low Voltage Switchroom Design Guide

Low voltage (LV) switchrooms are common across all industries and one of the more common spatial requirements which need to be designed into a project...

Cable Insulation Properties

Cable insulation is used to provide electrical separation between conductors of  a cable.  During the historical development of cables, numerous types...

Smarter Electrical Distribution

The other day I came across an article in Technology Review on the development of a smart transformer. A professor at North Carolina State University is...

8 Motor parts and common faults

Straight forward list of some common motor faults.  If I have missed any other common faults, please take a bit of time to add them in as a comment below...

Cables for MV Power Distribution - Earthed versus Unearthed Systems

Power cables can basically be classified into earthed and unearthed cables, where earthed and unearthed refer to the application for which the cable is...

Are We Losing Professional Integrity

I have been thinking recently that there appears to be less professional integrity around than when I first started my career in electrical engineering...

Fault Calculations - Typical Equipment Parameters

A frequent problem in fault calculations is the obtaining of equipment parameters.  While it is always preferable to use the actual parameters of the equipment...

Difference Between Live and Dead Tank Circuit Breakers

A quick post in connection with an email question: Live Tank - the circuit breaker the switching unit is located in an insulator bushing which is live...

Our website uses cookies so that we can provide a better experience.
To learn more about what cookies are and how to manage them visit AboutCookies.org