Single phase circuit on 3 phase current calc

Hi,

I have a question regarding calculating current in a 3 phase supply. I have my head around how to calculate the current in a 3 phase circuit. For example if we have a 22kw load assuming a power factor of 0.8 would be 22000/(1.732x415x0.8) = 38.25A

However if I’m installing a 7.2kw single phase circuit on a 3-phase supply I.e using L1 (or L2 or L3) and neutral. Is the calc 7200/(1.732x230x0.8) = 18.06 amps

It’s not the usual 7200/230 (simplified calc) where the current would be 31.30A we would use for a single phase supply?. Even though it is a single phase circuit?.

Thanks,

A.

asked 6/15/2019
spark83192
spark8319

2 Answers

Hi Steven,

I have a related question.  

We often utilize 240V 3PH to supply mixed 3PH loads and 1PH 240V loads on any two phases.

I want to confirm the calculation of current in the single phase loads at the line-to-line voltage in the following simplified example where the current for a single phase load of 1kVA = (1000VA / 2) / 240V = 2.08A (as opposed to 1000VA/240V = 4.17A).  The resulting system would then have a balanced 3PH load of approximately 9A.

 


Thanks.

 

answered 5 months ago tnhokie27 2
tnhokie27
edited 5 months ago
tnhokie272
tnhokie27

Looks like in your first example you are using 415 V, and 230 in your second.  The common convention is 415/240 or 400/230 V  [line-line/line-neutral].

This is how I like to calculate:

First example: 22000/0.8 = 27500 VA.  I =  (27500/3) / 240 = 38.2.  Same as your answer, just a slightly different way of calculating (and using 240 V, whereas 415/1.732 = 239.6 more accurately).  

Second example: 7200/0.8 = 90000VA = I = 9000/230 = 39.1 A.  

In your formulae using 1.732 x voltage assumes the voltage is line-line.  In the second example, the voltage is line-neutral. 

Hope this helps.

answered 6/16/2019 Steven McFadyen 246
Steven McFadyen

Your Answer

In order to provide an answer to this question, you must Login

I am flagging this question because...




10 inform moderator flags remaining

I am deleting this question because...




I am flagging this answer because...




10 inform moderator flags remaining

Flagging a Post

You have already flagged this post. Clicking "Remove Flag" below will remove your flag, thus reducing the count by one as well.

I am deleting this answer because...





Occam's Razor

I was reminded of Occam's Razor while reading a book. It's quite a simple principal of logic which has stood the test of time and is accepted as central...

8 Steps to Low Voltage Power Cable Selection and Sizing

A recurring theme on our forums is cable sizing. Now many installations are unique and require special consideration. However, a lot of the time things...

Tech Topics/Application Notes - Siemens

There are a lot of interesting two page type notes on various medium voltage topics – switchgear, circuit breakers, bus systems etc. It is on the Siemens...

DC Component of Asymmetrical Faults

The image (reproduced from IEC 60909) shows a typical fault in an ac system.  From the illustration it can seen that there is an initial dc component ...

Michael Faraday (the father of electrical engineering)

Famed English chemist and physicist Michael Faraday was born on September 22, 1791, in Newington Butts, a suburb of Surrey just south of the London Bridge...

Closed Doors

"I can live with doubt and uncertainty and not knowing. I think it is much more interesting to live not knowing than to have answers that might be wrong...

How to Write an Electrical Note

Electrical notes are a collaborative collection of electrical engineering information and educational material. Any registered user can add content. ...

Voltage Drop in Installations - Concepts

Problems on achieving maximum voltage drop within an installation come up often. Depending where you live, local regulations will have different limits...

Bows and Arrows

It starts with me reading one of the Horrible History books with my son (Groovy Greeks). Arrows were mentioned which lead to the discussion of the bodkin...

What does N+1 mean?

The term 'N+1' relates to redundancy and simply means that if you required 'N' items of equipment for something to work, you would have one additional...

Our website uses cookies so that we can provide a better experience.
To learn more about what cookies are and how to manage them visit AboutCookies.org