Single phase circuit on 3 phase current calc

Hi,

I have a question regarding calculating current in a 3 phase supply. I have my head around how to calculate the current in a 3 phase circuit. For example if we have a 22kw load assuming a power factor of 0.8 would be 22000/(1.732x415x0.8) = 38.25A

However if I’m installing a 7.2kw single phase circuit on a 3-phase supply I.e using L1 (or L2 or L3) and neutral. Is the calc 7200/(1.732x230x0.8) = 18.06 amps

It’s not the usual 7200/230 (simplified calc) where the current would be 31.30A we would use for a single phase supply?. Even though it is a single phase circuit?.

Thanks,

A.

asked 6/15/2019
spark83192
spark8319

2 Answers

Looks like in your first example you are using 415 V, and 230 in your second.  The common convention is 415/240 or 400/230 V  [line-line/line-neutral].

This is how I like to calculate:

First example: 22000/0.8 = 27500 VA.  I =  (27500/3) / 240 = 38.2.  Same as your answer, just a slightly different way of calculating (and using 240 V, whereas 415/1.732 = 239.6 more accurately).  

Second example: 7200/0.8 = 90000VA = I = 9000/230 = 39.1 A.  

In your formulae using 1.732 x voltage assumes the voltage is line-line.  In the second example, the voltage is line-neutral. 

Hope this helps.

answered 6/16/2019 Steven McFadyen 246
Steven McFadyen

Hi Steven,

I have a related question.  

We often utilize 240V 3PH to supply mixed 3PH loads and 1PH 240V loads on any two phases.

I want to confirm the calculation of current in the single phase loads at the line-to-line voltage in the following simplified example where the current for a single phase load of 1kVA = (1000VA / 2) / 240V = 2.08A (as opposed to 1000VA/240V = 4.17A).  The resulting system would then have a balanced 3PH load of approximately 9A.

 


Thanks.

 

answered 4 months ago tnhokie27 2
tnhokie27
edited 4 months ago
tnhokie272
tnhokie27

Your Answer

In order to provide an answer to this question, you must Login

I am flagging this question because...




10 inform moderator flags remaining

I am deleting this question because...




I am flagging this answer because...




10 inform moderator flags remaining

Flagging a Post

You have already flagged this post. Clicking "Remove Flag" below will remove your flag, thus reducing the count by one as well.

I am deleting this answer because...





Three Phase Current - Simple Calculation

The calculation of current in a three phase system has been brought up on our site feedback and is a discussion I seem to get involved in every now and...

Aluminium Windings - Dry Type Transformers

The other day I was talking to a colleague who is a building services consultant.  Despite regularly specifying dry-type/cast resin transformers he was...

IEC Reference Designations

The IEC publishes a series of documents and rules governing the preparation of documents, drawings and the referencing of equipment.   Depending on country...

Multimeter

Multimeters are undoubtedly the most common item of electrical test equipment in use.  Often it is the first piece of equipment people will turn to when...

myElectrical - Cable Sizing Tool Upgrade

Our IEE cable sizing was wrote a few years ago and had become rough around the edges. I thought it was time to give the tool a service. Unfortunately when...

Alternating Current Circuits

Alternating current (a.c.) is the backbone of modern electrical power distribution. In this article I’ll be pulling some of the more important concepts...

Occam's Razor

I was reminded of Occam's Razor while reading a book. It's quite a simple principal of logic which has stood the test of time and is accepted as central...

Network Theory – Introduction and Review

In electrical engineering, Network Theory is the study of how to solve circuit problems. By analyzing circuits, the engineer looks to determine the various...

Voltage Levels – Confused?

I was having a conversation the other day about voltage levels.  While everyone was in agreement that low voltage was 1000 V and less, there was more confusion...

1,000 kV UHV First for China

At the beginning of the year China put the world's first 1,000 kV UHV transmission system into operation. Transmitting power at over a million volts is...

Our website uses cookies so that we can provide a better experience.
To learn more about what cookies are and how to manage them visit AboutCookies.org