Limitation of AC Submarine Cable

I know Capacitance charging current is given by the equation:
Ic= 2PICE
PI=3.14 approx.
C = Capacitance
E = Voltage

How would you calculate what the maximum length of a submarine cable before losses are to great? Is there an example of this calculation?
I'm trying to determine how to determine and calculate whether a AC submarine cable would be suitable for installation. Would you look at the Capacitance charging current? if so what are you comparing it with?
Thank You.

asked 4/3/2012
Mjomah6
Mjomah

1 Answer

Although capacitance has its effects inductance and resistance too will have their impact on VD. Refer cable manufacturer's cataloque
answered 5/16/2012 naban 6
naban

Your Answer

In order to provide an answer to this question, you must Login

I am flagging this question because...




10 inform moderator flags remaining

I am deleting this question because...




I am flagging this answer because...




10 inform moderator flags remaining

Flagging a Post

You have already flagged this post. Clicking "Remove Flag" below will remove your flag, thus reducing the count by one as well.

I am deleting this answer because...





Maxwell's Equations - Introduction

Maxwell's Equations are a set of fundamental relationships, which govern how electric and magnetic fields interact. The equations explain how these fields...

UPS - Uninterruptible Power Supply

A UPS is an uninterruptible power supply.  It is a device which maintains a continuous supply of electrical power, even in the event of failure of the...

Motor Insulation

Insulation on a motor prevents interconnection of windings and the winding to earth.  When looking at motors, it is important to understand how the insulation...

Power Factor

Power factor is the ratio between the real power (P in kW) and apparent power (S in kVA) drawn by an electrical load. The reactive power (Q in kVAr)...

Questions - Reputation and Privilege

Our question and answer system while letting you do exactly what it says, is much more.  It is a dynamic user driven system, where our users not only ask...

Electromagnetic Fields - Exposure Limits

Exposure to time varying magnetic fields, from power frequencies to the gigahertz range can have harmful consequences.  A lot of research has been conducted...

What happened to the cable notes?

If you are wondering what happened to our cable notes, the short answer is that we have moved them to myCableEngineering.com.  The "Knowledge Base" at...

Motor Efficiency Classification

Electric motors are one of the most widely used items of electrical equipment. Improving motor efficiency benefits include, reduced power demand, lower...

Fault Calculations - Typical Equipment Parameters

A frequent problem in fault calculations is the obtaining of equipment parameters.  While it is always preferable to use the actual parameters of the equipment...

RLC Circuit, Resistor Power Loss - some Modelica experiments

Modelica is an open source (free) software language for modelling complex systems. Having never used it before, I thought I would download a development...

Our website uses cookies so that we can provide a better experience.
To learn more about what cookies are and how to manage them visit AboutCookies.org