Aluminium Windings - Dry Type Transformers 

By on

The other day I was talking to a colleague who is a building services consultant.  Despite regularly specifying dry-type/cast resin transformers he was unaware that many manufacturers use aluminium for the windings; I think Siemens exclusively use aluminium and don’t offer copper anymore.  To confirm this he promptly phoned Schneider Electric and was informed that they use aluminium (or copper on request).

This reminded me of a few years ago when I was working for a contractor and wanted to install Siemens transformers on a large international airport.  Siemens was one of the three preferred vendors; however the airport’s specification called for copper windings.  Because of the specification the airport refused the transformers for weeks (we even had the Siemens factory guys out from Germany).  The client’s agreement in the end was not driven by technical considerations, but by contractual/time delay issues.  Transformers were installed and as far as I know are still happily humming away.

The illustration of a Siemens GEAFOL transformer shows the HV and LV aluminium windings.  The HV windings are wound from aluminium foil interleaved with an insulating foil.  The LV windings are wound form single-aluminium sheets and interleaved with cast-resin impregnated fibreglass fabric. Foil type windings are subject to less electrical stress than conventional windings resulting in higher AC and impulse voltage withstand characteristics.  Thermal expansion coefficients of aluminium and cast resin are similar and resulting thermal stress due to load change is kept to a minimum.

To my mind, compliance with the performance requirements of the manufacturing standards is the important criteria and the constructional aspects (aluminium or copper) are not that significant. As a final practical tip, during the above airport installation copper cable was being terminated onto the aluminium terminals of the transformer.  In this instance bi-metallic plates were inserted between the cable lugs and transformer terminals.



Steven McFadyen's avatar Steven McFadyen

Steven has over twenty five years experience working on some of the largest construction projects. He has a deep technical understanding of electrical engineering and is keen to share this knowledge. About the author

myElectrical Engineering

comments powered by Disqus

  1. ManjoloPhiri's avatar ManjoloPhiri says:
    9/1/2011 2:11 PM

    The only reason I would allow the use of Alluminium windings in a transformer is the price difference between copper and alluminum. Copper is the best material so far for transformer windings whatever electrical parameters you consider! Please transformer manufacturers continue using copper afterall the price is now down!

    • Steven's avatar Steven says:
      9/1/2011 2:11 PM

      My aluminium winding experience has been with Siemens because they only manufacture aluminium windings. Have to say that I have never had any problems and the transformers work great. Of course copper windings also work great (to me both are acceptable). Talking of problems and a bit off topic, I also think that when selecting a transformer it needs to be suitable for the intended environment/loading and that surge arrestors if used are correctly sized. I have recently come across an instance where this was not done and they have had several transformer failures.

  2. rommel's avatar rommel says:
    9/1/2011 2:11 PM

    Which material, element is more conductive? copper or aluminium?

    • Steven's avatar Steven says:
      9/1/2011 2:11 PM

      Copper is the better conductor. Although Aluminum is still pretty good as a conductor.

  3. Paul's avatar Paul says:
    12/28/2012 2:57 PM

    How the bi-metallic plates can eliminate the ionization potential between two type of metal?

    • Steven's avatar Steven says:
      1/13/2013 7:41 AM

      Bimetallic plates prevent corrosion which could result from a direct connection of two dissimilar metals (aluminum and copper in this case).


Comments are closed for this post:
  • have a question or need help, please use our Questions Section
  • spotted an error or have additional info that you think should be in this post, feel free to Contact Us



Aluminium Windings - Dry Type Transformers

The other day I was talking to a colleague who is a building services consultant.  Despite regularly specifying dry-type/cast resin transformers he was...

Cables for MV Power Distribution - Earthed versus Unearthed Systems

Power cables can basically be classified into earthed and unearthed cables, where earthed and unearthed refer to the application for which the cable is...

Frame Leakage Protection

While not as popular as it once was, frame leakage protection does still have some use in some circumstances.  In essence frame leakage is an earth fault...

Fault Calculation - Per Unit System

Per unit fault calculations is a method whereby system impedances and quantities are normalised across different voltage levels to a common base.  By removing...

Questions - Reputation and Privilege

Our question and answer system while letting you do exactly what it says, is much more.  It is a dynamic user driven system, where our users not only ask...

Introduction to Cathodic Protection

If two dissimilar metals are touching and an external conducting path exists, corrosion of one the metals can take place.  Moisture or other materials...

Maxwell's Equations - Introduction

Maxwell's Equations are a set of fundamental relationships, which govern how electric and magnetic fields interact. The equations explain how these fields...

Operational Amplifier

The fundamental component of any analogue computer is the operational amplifier, or op amp. An operational amplifier (often called an op-amp,) is a high...

Thermoplastic and Thermosetting Insulation

While there are a vast array of cable insulation materials, these are often divided into two general types; Thermoplastic or Thermosetting. For example...

Autonomous Vehicle Challenge

Two driverless and solar power vans have departed from Italy on their way to China via the silk road. During the 13,000 kM trip the vans will drive themselves...

Have some knowledge to share

If you have some expert knowledge or experience, why not consider sharing this with our community.  

By writing an electrical note, you will be educating our users and at the same time promoting your expertise within the engineering community.

To get started and understand our policy, you can read our How to Write an Electrical Note